No problem here. That is precisely one of the many benefits of the forum. Now if someone else couldve said it before me, I wouldve liked that better. Good thing I always use tee's w/plugs, huh?
Bobby Gillett Sr. Project Manager Key Fire Protection, Inc. (731) 424-0130 office (731) 424-9285 fax (731) 267-4853 cell [email protected] -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Thom McMahon Sent: Wednesday, March 17, 2010 1:11 PM To: [email protected] Subject: RE: dry pendent's on flex drops I only responded to begin with because I just saw a job where the DP were screwed into the bottom of 3" BL with weld outlets, and the AHJ asked how it should have been done. We're all here to learn, if I could just give up being wrong so often then I wouldn't need this forum. Well no hope there, carry on all. Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Bobby Gillett Sent: Wednesday, March 17, 2010 12:00 PM To: [email protected] Subject: RE: dry pendent's on flex drops You are correct, sorry for any confusion I put in anyone's brain for that short period and thank you Thom for catching that and correcting me. Bobby Gillett Sr. Project Manager Key Fire Protection, Inc. (731) 424-0130 office (731) 424-9285 fax (731) 267-4853 cell [email protected] -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Thom McMahon Sent: Wednesday, March 17, 2010 12:44 PM To: [email protected] Subject: RE: dry pendent's on flex drops Bobby, you may want to look at that again, the DS-1 only allows you to use a 1"CPVC x 1"FM adapter by Tyco in wet systems, and suggests the use of Fig. 12 for wet systems, nowhere does it allow the use of a coupling. Wet or Dry. Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Bobby Gillett Sent: Wednesday, March 17, 2010 11:38 AM To: [email protected] Subject: RE: dry pendent's on flex drops In a WET pipe system Tyco DS-1 allows the use of a 1x1 NPT female adapter. I should've said when listing allows after my statement. Bobby Gillett Sr. Project Manager Key Fire Protection, Inc. (731) 424-0130 office (731) 424-9285 fax (731) 267-4853 cell [email protected] -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Thom McMahon Sent: Wednesday, March 17, 2010 12:15 PM To: [email protected]; [email protected] Subject: RE: dry pendent's on flex drops It's been a while since I looked at ALL MFG.'s literature for Dry Pend. But I don't recall any that were OK to screw into a coupling. What brand are you using bobby? Thom McMahon, SET Firetech, Inc. 2560 Copper Ridge Dr P.O. Box 882136 Steamboat Springs, CO 80488 Tel: 970-879-7952 Fax: 970-879-7926 Subject: RE: dry pendents on flex drops Or a coupling, but all of the flex drops I have seen have a ¾ or ½ reducer on the end. Bobby Gillett Sr. Project Manager Key Fire Protection, Inc. (731) 424-0130 office (731) 424-9285 fax (731) 267-4853 cell [email protected] Subject: Re: dry pendents on flex drops I don't think they will fit the DP needs to be installed into a tee. ------Original Message------ From: Todd Williams _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) No virus found in this incoming message. Checked by AVG - www.avg.com Version: 9.0.791 / Virus Database: 271.1.1/2752 - Release Date: 03/17/10 02:33:00 _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) No virus found in this incoming message. Checked by AVG - www.avg.com Version: 9.0.791 / Virus Database: 271.1.1/2752 - Release Date: 03/17/10 02:33:00 _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) No virus found in this incoming message. Checked by AVG - www.avg.com Version: 9.0.791 / Virus Database: 271.1.1/2752 - Release Date: 03/17/10 02:33:00 _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)