Standard sidewall sprinklers are only allowed under smooth, flat ceilings.
(NFPA 13 8.4.2--2002 edition.) Although I see them all the time under open
wood framing.  But that doesn't make it right.  You have an obligation to
point out to the building owner that the existing system is not correct and
install the new addition correctly.  IMO.

Michael Ricks
Katco Fire Sprinkler Design
P.O. Box 607
555 South 100 East
Salem, UT   84653
801-423-3096  Cell:  801-380-4651
 

-----Original Message-----
From: Travis Mack, SET [mailto:[email protected]] 
Sent: Wednesday, March 17, 2010 8:47 AM
To: [email protected]
Cc: [email protected]
Subject: Re: HSW vs SD1 attic sprinkler

This is an addition to a system that another contractor did.  I think 
that the layout is incorrect and just trying to figure a way to get the 
new addition done correct.

On 3/17/2010 7:43 AM, [email protected] wrote:
> Travis,
>   The table 8.7.2.2.1 in the 2002 edition of NFPA 13 only allows a 12 ft.
throw and a maximum spacing of 120 sq.ft. in your situation.You may have a
problem with the standard sidewalls unless you are required to use a more
recent standard that may be different than this.
>
>
> ---- "Travis Mack wrote:
>    
>> We are doing an addition to a project.  The roof is a mansard type roof,
>> combustible framing, trusses 2' on center with a 4:12 slope.  The
>> distance along the slope is 14'.  Has anyone ever heard of using
>> sidewall sprinklers installed at the peak, shooting down the slope for
>> this?  The sidewall sprinklers are spaced at +/- 12'x12'.  I always
>> assumed you would need SD1 sprinklers for this type of arrangement.
>> Also, if you use the HSW, wouldn't you need 20 psi end head pressure
>> because you are>8' on center going through the trusses when the roof
>> slope is 4:12?
>>
>> -- 
>> Please feel free to call if you have any questions or comments.
>>
>> Sincerely,
>>
>> Travis Mack, SET
>> MFP Design, LLC
>> 2508 E Lodgepole Drive
>> Gilbert, AZ 85298
>> Office (480) 505-9271
>> Fax (866) 430-6107
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email to:[email protected]
>> (Put the word unsubscribe in the subject field)
>>      


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to