Thank you for the clarification Roland!

Damien Shannon.

QED Sprinkler Designs, Inc.
2836 N. Drake Ave,
Unit: Coach House
Chicago, IL. 60618
Phone: (773) 704 2571
Fax: (866) 308 1367


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Roland
Huggins
Sent: Tuesday, March 23, 2010 11:35 AM
To: [email protected]
Subject: Re: Room Design vs. Adjacent Hazards

The example is focused on the big question of the size of the remote  
area but it applies OH-II and EH-I and defines the boundary line  
between them.  Since that is what drives the installation criteria,  
it's all aspects of the design basis.

Roland

On Mar 23, 2010, at 1:48 AM, Damien Shannon wrote:

> Roland,
>
> Since you were there:), could you please clarify the intent of the  
> committee
> for 11.1.2 in regards to spacing? The verbiage in the standard states
> '...the required sprinkler protection...' which literally would seem  
> to
> include all requirements of the sprinkler protection, i.e. spacing and
> hydraulic criteria. But since it is in the Design Approaches chapter  
> (aka,
> hydraulic approaches chapter) I am a little unsure if the statement is
> indeed intended to relate to the spacing and hydraulic criteria or  
> only to
> relate to the hydraulic criteria.
>
> Any insight would be appreciated.
>
> Damien Shannon.
>
> QED Sprinkler Designs, Inc.
> 2836 N. Drake Ave,
> Unit: Coach House
> Chicago, IL. 60618
> Phone: (773) 704 2571
> Fax: (866) 308 1367
>
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Roland
> Huggins
> Sent: Monday, March 22, 2010 5:54 PM
> To: [email protected]
> Subject: Re: Room Design vs. Adjacent Hazards
>
> the problem is that you are reading it with a interpretation in mind
> from a quick initial read.  Ed hit it on the nose although using EH
> and LH is a better example since the size of the RA differs.  As
> others have said - read the Annex which provides examples.
>
> Granted when we said (we being the TC but I was on the task group that
> developed this concept in 99 - look in the HAndbook not the standard)
> SPRINKLER PROTECTION it does imply the presence of sprinklers,  We
> should have said sprinkler CRITERIA.
>
> It does not replace the Room Design method. If it isn't crystal clear
> after studying the annex, give me a call.
>
> Roland
>
> Since I invoked the name of the omnipotent TC, I should chant the TC
> member mantra - this is not to b considered a formal interpretation of
> NFPA or its TC.  Not to be equated with the infamous lines - We're
> from the federal government. We're here to help you.
>
> On Mar 22, 2010, at 1:45 PM, Richardson, R wrote:
>
>> Thanks for the thoughts.
>>
>> However, the way section 11.1.12 is written, there is no pointer to
>> the room design requirements as being applicable as well.
>>
>> In effect you seem to be saying that section 11.1.2 is not allowed
>> unless each side of the wall is large enough to facilitate a full
>> operating area (with allowable reductions of course) per NFPA13.
>>
>> I am having trouble reaching that conclusion based on the language
>> in the standard.
>>
>> Intent versus what was actually written I suppose, but usually in my
>> world the actual language overrides the intent, except in the case
>> of imminent life safety hazard, likely not the case here.
>>
>> Rich
>>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>
> __________ Information from ESET Smart Security, version of virus  
> signature
> database 4966 (20100322) __________
>
> The message was checked by ESET Smart Security.
>
> http://www.eset.com
>
>
>
>
> __________ Information from ESET Smart Security, version of virus  
> signature
> database 4966 (20100322) __________
>
> The message was checked by ESET Smart Security.
>
> http://www.eset.com
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

__________ Information from ESET Smart Security, version of virus signature
database 4967 (20100323) __________

The message was checked by ESET Smart Security.

http://www.eset.com


 

__________ Information from ESET Smart Security, version of virus signature
database 4967 (20100323) __________

The message was checked by ESET Smart Security.

http://www.eset.com
 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to