Are there any standard spray 165* glass bulb heads available? Why are the strut 
heads 165 and glass bulb 155?
I need to know if the 165s are available, if anyone knows please. 
I tried posting this earlier but I don't think it went through 
Thank you 

Forest Wilson 
Cherokee Fire 

Sent from my Verizon Wireless Phone

----- Reply message -----
From: "Forest Wilson" <cherokeefire...@aol.com>
Date: Mon, Mar 29, 2010 3:43 PM
Subject: 500 DEGREE OVEN
To: <sprinklerforum@firesprinkler.org>

Probably because sprinkler water would reach temperatures in excess of 120*
(7.7.1.3.1.1) That pertains to combination systems, but I think there's a
similar requirement for standard wet systems.


Forest Wilson

Project Manager
Cherokee Fire Protection Co.
1855 Bellbrook Ave Ste C
Xenia OH 45385

PH 937-376-2333
FX 614-455-4324

visit our blog: www.cherokee-fire.blogspot.com


NOTICE: The information contained in this email is intended to be solely for
the use of the named individual or entity to which it is directed and may
contain information that is privileged or otherwise confidential. It is not
intended for transmission to, or receipt by, anyone other than the named
addressee (or a person authorized to deliver it to the named addressee). It
should not be copied or forwarded to any unauthorized persons. If you have
received this electronic mail transmission in error, please delete it from
your system without copying or forwarding it, and notify the sender of the
error by reply email or by calling Cherokee Fire Protection Co. at
888-347-3079 toll free.




-----Original Message-----
From: sprinklerforum-boun...@firesprinkler.org
[mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Robert
Thompson
Sent: Monday, March 29, 2010 3:36 PM
To: sprinklerforum@firesprinkler.org
Subject: 500 DEGREE OVEN

Has anyone had a problem with installing a wet sprinkler in a high temp.
oven approx. 500 degrees.  The piping is on the exterior and a drop
sprinkler into the oven.   An FM plan reviewer stated that FM suggests
using a dry system when temps run this high.
 

Thank you 
 Robert  Thompson 

 DAKOTA 
FIRE PROTECTION 
1710 N. Washington Street 
Grand Forks ND 58206-5327 
Phone # (701) 772-8820 
Fax # (701) 772-7932 
Email rob...@dakotafire.com 

 
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
Sprinklerforum@firesprinkler.org
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: supp...@firesprinkler.org

To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org
(Put the word unsubscribe in the subject field)

Reply via email to