Kevin, That's the beauty of this forum. It is generally a group that can help but never (rarely) tries to stuff crow down our throats when we've missed something. That is unless it's Church or Leyton, those guys are ruthless!! :)
Cliff Whitfield, SET Fire Design, Inc. 3784 Holly Ridge Trail Marianna, FL 32448 Phone: 850-526-1886 Fax: 850-526-1884 Cell: 850-557-1886 www.fire-design.com -----Original Message----- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Law, Kevin W Sent: Wednesday, March 31, 2010 2:26 PM To: sprinklerforum@firesprinkler.org Subject: RE: Underground flushing velocities You are correct the word any does not appear in the text. I guess my comment was slanted from the view that in the text for NFPA 24-1995. "The minimum rate of flow shall be not less than the water demand rate of the system, which is determined by the system design, or not less than that necessary to provide a velocity of 10 ft/s , whichever is greater." The standard changed on the next revision to it's present wording......... I find that crow is best eaten while it is still warm, it sticks in your throat less Kevin Law, PE Bechtel National, Inc. Waste Treatment Project Fire Protection Engineering Work (509) 371-3280 Cell (509) 531-5715 -----Original Message----- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Ed Kramer Sent: Wednesday, March 31, 2010 11:09 AM To: sprinklerforum@firesprinkler.org Subject: RE: Underground flushing velocities With all due respect, I don't see the word 'any' anywhere in 10.10.2.1.3. I'm looking at the 2010 version, maybe older versions contain the word 'any'. Ed Kramer Littleton, CO > -----Original Message----- > From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum- > boun...@firesprinkler.org] On Behalf Of Law, Kevin W > Sent: Wednesday, March 31, 2010 11:38 AM > To: sprinklerforum@firesprinkler.org > Subject: RE: Underground flushing velocities > > The key is the requirement states it shall not be less than ANY one of > the following. > > Therefore, the very minimum flow rate will be 10ft/sec line velocity. > > If your system cannot under any condition flow a minumum of 10ft/sec > then you would have to get a ruling from the AHJ to allow that. > > Nuff said > > > Kevin Law, PE > Bechtel National, Inc. > Waste Treatment Project > Fire Protection Engineering > Work (509) 371-3280 > Cell (509) 531-5715 _______________________________________________ Sprinklerforum mailing list Sprinklerforum@firesprinkler.org http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: supp...@firesprinkler.org To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list Sprinklerforum@firesprinkler.org http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: supp...@firesprinkler.org To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list Sprinklerforum@firesprinkler.org http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: supp...@firesprinkler.org To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org (Put the word unsubscribe in the subject field)