negative.  If they were 7-1/2 ft on center, it would be acceptable  
since that meets the definition for smooth ceiling (within each  
individual channel that is).  Look at A.3.7.2 (3)(b) - page 244 may be  
faster.

Roland

On Apr 1, 2010, at 1:55 PM, Ryan Peterson wrote:

> If I have concrete tee construction (28" deep and 6'-0" OC), is it  
> within the listing of any sidewall (standard, ext coverage or  
> residential) to install 1 sidewall per "bay" spraying down the  
> length of the channel formed between the tees or between a tee and a  
> wall?
>
> Thanks,
>
> Ryan Peterson
> Wayne Automatic Fire Sprinklers
> 222 Capitol Court, Ocoee Fl. 34761
>
>
>