Since your pump is not listed, you don't comply with NFPA 20 so why does it matter if the standard allows an automatic shut off? For your use, the 2010 edition of NFPA states the following:
12.7.2.6 Sole Supply Pumps. 12.7.2.6.1 Shutdown shall be accomplished by manual or automatic means. 12.7.2.6.2 Automatic shutdown shall not be permitted where the pump constitutes the sole source of supply of a fire sprinkler or standpipe system or where the authority having jurisdiction has required manual shutdown. Regardless of the pump listing or other compliance issues, the answer lies solely with the permission of the local AHJ. Important Notice: As a member of the NFPA 13 Installation & NFPA 25 Committee's, this correspondence is not a Formal Interpretation issued pursuant to NFPA Regulations. Any opinion expressed is the personal opinion of the author, and does not necessarily represent the official position of the NFPA or its Technical Committees. In addition, this correspondence is neither intended, nor should be relied upon, to provide consultation or services. Bob Caputo -----Original Message----- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of sam b Sent: Sunday, April 11, 2010 11:15 PM To: sprinklerforum@firesprinkler.org Subject: FIRE PUMP: Urgent Dear all.. We are in the process of installing *temporary fire protection* for a 30 story builing. The pump installed is a *single diesel engine pump* (Not listed) for the supplying water for the landing valves in each floor.The fire pump is located in the basement floor and is barricaded . The operation of the fire pump will be such that In case of pressure drop due to opening of the hosereeel or landing valves the pump will start. Now during the inspection from Client,they asked us why there is no automatic shutoff . *The scenario they are considering is *. Suppose some labour accidentally opens the hosreel for anypurpose,the pump will start running and if there is noone to stop the pump ,will it get damaged.? I suggested we could provide a fire alarm bell for alerting the people. *Can we provide automatic shuttoff for the diesel pump. Is it acceptable as per NFPA?* Is there anyother options available or anything from NFPA to support that we dont need automatic shutoff? Please give your valuable inputs. Sam _______________________________________________ Sprinklerforum mailing list Sprinklerforum@firesprinkler.org http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: supp...@firesprinkler.org To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list Sprinklerforum@firesprinkler.org http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: supp...@firesprinkler.org To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org (Put the word unsubscribe in the subject field)