SSU are not specifically listed for CC spaces less than 36" in depth. They are listed for CC spaces though. Which is what drove the manufacturers to produce the "CC" heads.
Thanks, Eric Tysinger CET NICET III - 108988 Designer Wayne Automatic Fire Sprinklers, Inc. 4370 Motorsport Drive Concord, NC 28027 p: (704)782-3032 x1751 f: (704)795-6838 C: (239)633-9703 -----Original Message----- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Matt Grise Sent: Wednesday, April 14, 2010 10:52 AM To: 'sprinklerforum@firesprinkler.org' Subject: RE: CC sprinklers It says that the heads must be listed for such use [the scenario outlined in 13 8.14.1.6 2002]. Are SSU heads not listed for such use? Matt Grisé PE*, LEED AP Sales Engineer Alliance Fire Protection *Licensed in KS & MO 913.888.0647 ph 913.888.0618 f 913.927.0222 cell www. AFPsprink.com -----Original Message----- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Eric Tysinger Sent: Wednesday, April 14, 2010 9:50 AM To: sprinklerforum@firesprinkler.org Subject: RE: CC sprinklers 8.14.1.6 states "horizontal combustible concealed spaces". There is no reference to exclude trusses, joists or TJI's. Unless I am missing something. Thanks, Eric Tysinger CET NICET III - 108988 Designer Wayne Automatic Fire Sprinklers, Inc. 4370 Motorsport Drive Concord, NC 28027 p: (704)782-3032 x1751 f: (704)795-6838 C: (239)633-9703 -----Original Message----- From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum-boun...@firesprinkler.org] On Behalf Of Ed Kramer Sent: Wednesday, April 14, 2010 10:28 AM To: sprinklerforum@firesprinkler.org Subject: RE: CC sprinklers Tony, it may sound a bit nit-picking, but NFPA 13 only requires CC sprinklers when the space has wood trusses or wood joists. You have TJI's, so you don't have to use them - use standard-spray QR heads. Is that crazy? Yea, but that's the way it's written. The commentary in the handbook gives supports to the above. Ed Kramer Littleton, CO > -----Original Message----- > From: sprinklerforum-boun...@firesprinkler.org [mailto:sprinklerforum- > boun...@firesprinkler.org] On Behalf Of A.P.Silva > Sent: Friday, May 14, 2010 10:41 PM > To: sprinklerforum@firesprinkler.org > Subject: CC sprinklers > > > NFPA has requirements for combustible concealed space sprinklers. > However, > the TYCO CC sprinklers have their own restrictions on the application. > Such > as, to be used for light hazard only. If used with TJI's, the TJI > space has to be filled with non-combustible insulation etc. What > happens if these restrictions don't apply. Use standard heads? Or use > CC heads regardless, as they are required by NFPA? > > What I have is a 24" to 36" deep crawlspace, the ceiling of which > comprises of TJI's which are exposed to the space below. The > insulation is on the floor and not in the TJI space. The building is a > school, but specd. To be designed for OH 1. Any comments? > > Also, any other manufacturer's for CC heads? > > Tony > > _______________________________________________ > Sprinklerforum mailing list > Sprinklerforum@firesprinkler.org > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > For Technical Assistance, send an email to: supp...@firesprinkler.org > > To Unsubscribe, send an email to:Sprinklerforum- > requ...@firesprinkler.org (Put the word unsubscribe in the subject > field) _______________________________________________ Sprinklerforum mailing list Sprinklerforum@firesprinkler.org http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: supp...@firesprinkler.org To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list Sprinklerforum@firesprinkler.org http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: supp...@firesprinkler.org To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list Sprinklerforum@firesprinkler.org http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: supp...@firesprinkler.org To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list Sprinklerforum@firesprinkler.org http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: supp...@firesprinkler.org To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org (Put the word unsubscribe in the subject field)