Where are the raw materials coming from?   Are they conveyed from different 
areas for assembly?  We know where the finished kits are stored and how they 
are produced by your description but not where the input materials are coming 
from or how they are handled.


So you need to look at the whole picture, form the point where the truck 
unloads the input materials, the assembly of materials and then the final 
handling and packaging and storage for shipment.

Also be careful, some gowns are more of a plastic type material than cloth, and 
sponges as well can at times be one of the foam classes.  So you might have 
more plastics in the package than you thought. Unless they are cloth bandages, 
"band-aide" type bandages are about 1/2 plastic type material. You need 
specific information on the commodities.  

Are the kits put in cardboard boxes?

Any pallet storage?






Craig L. Prahl, CET   
Fire Protection Specialist
Mechanical Department
CH2MHILL
Lockwood Greene
1500 International Drive
PO Box 491, Spartanburg, SC  29304-0491
Direct - 864.599.4102
Fax - 864.599.8439
[email protected]
http://www.ch2m.com 


-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Michael J. Ricks
Sent: Monday, April 26, 2010 11:18 AM
To: [email protected]
Subject: Ordinary Hazard Group 1 vs. Group 2

I am currently working on a project that assembles medical kits for use in 
hospitals.  The kits include mostly group III commodities (paper sheets, 
sponges, bandages, gowns with a small amount (less than 4% by weight) of 
plastic bowls and trays.  The materials for these kits as well as the finished 
kits are stockpiled in a warehouse area separate from the assembly area.  There 
is no stock piling of any material in the assembly room.  The material comes in 
and leaves on conveyer belts.

 

Based on the definition of Ordinary Hazard Group 1 in NFPA 13 5.3 (2002) I have 
classified this area as a group 1 occupancy.  I have based this on the fact 
that there is no stockpiles of material and that the products are a class III 
commodity (since a class IV commodity would need to be at least 5%
Group A plastics by weight).   According to the Automatic Sprinkler Systems
Handbook (2002) page 81, "Group 1 occupancies are mostly light manufacturing 
and service industries were the use of flammable and combustible liquids or 
gases is either nonexistent or very limited.  Stock piles of combustible 
commodities typically found within and ordinary hazard group 1 occupancy cannot 
exceed a height of 8 ft.  additionally, the quantity and arrangement of the 
stockpiles cannot exceed the limitations of miscellaneous storage as defined in 
Chapter 3.The ordinary hazard group 2 classification addresses those ordinary 
hazard occupancies that do not meet the criteria of the group
1 classifications"  I felt that the assembly of these kits fit nicely with this 
description.

 

The AHJ feels that the "combustibility" of class III commodities would mandate 
group 2.  I have pointed out that many of the examples of group 1 occupancies 
listed in NFPA 13 (laundries, dairy products processing, electronics plants, 
bakeries, and canneries) either use or product class III commodities.  I feel 
that the guidance given in the handbook relating to flammable liquids and gases 
should be the standard in determining combustibility.  

 

Anyway, thought I would throw this out there and see if anyone could give me 
any guidance or resources-or show me that I am off base.  

 

Just so everyone understands, we want to use extended coverage heads with 20 x 
20 spacing.  The existing system easily supports group 1 but will not support 
group 2.

 

Thanks,

 

Michael Ricks

Katco Fire Sprinkler Design

P.O. Box 607

555 South 100 East

Salem, UT   84653

801-423-3096  Cell:  801-380-4651

[email protected]

 

 

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to