Depending on the building, I calculated 3 in the remote compartment (a
Marriott 13R 4 stories) but also included 5 spkrs in the corridor as it
served non-dwelling areas also (NFPA #13 2002, 11.2.3.3.6)

On Fri, May 28, 2010 at 3:23 PM, David Blackwell <[email protected]> wrote:

> Note Roland states "Could": Depending on circumstances [and how
> knowledgeable the AHJ is in hydraulics], you may need to submit both a 1
> head and a multi-head calculation to prove to the AHJ what is the most
> demanding.
>
>
>
> David W. S. Blackwell, II, PE, CFI-I, CFPE
> Engineering
> ----------------------------------------------------------------
> Office of State Fire Marshal
> 141 Monticello Trail
> Columbia, SC 29203
> Phone:  803.896.9833
> Fax:  803.896.9806
> Email:  [email protected]
> OSFM Website: http://www.llr.state.sc.us/firemarshal.asp
> ----------------------------------------------------------------
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Roland
> Huggins
> Sent: Friday, May 28, 2010 3:17 PM
> To: [email protected]
> Subject: Re: How Many Heads to calc for 13D & 13R
>
> 13D says ALL sprinklers in the compartment UP to a maximum of two
> sprinklers.
> 13R says the same but up to a maximum of four.
> So it could be a single sprinkler calculation for either.
>
> Roland
>
> On May 28, 2010, at 11:39 AM, Richardson, R wrote:
>
> > I had always thought that both NFPA 13R and 13D required a minimum
> > two head calculation.
> >
> > For various reasons we were actually reading it today and notice
> > that there does not appear to be a minimum number of heads to calc,
> > just calc. how many heads are in a compartment.
> >
> > We have an apartment whose units have 1 head per compartment, is it
> > acceptable to do a 1 head calc for 13R?
> >
> > Thanks,
> >
> > Rich Richardson
> > Seattle Fire Department
> >
> >
> > _______________________________________________
> > Sprinklerforum mailing list
> > [email protected]
> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
> >
> > For Technical Assistance, send an email to: [email protected]
> >
> > To Unsubscribe, send an email
> to:[email protected]<to%[email protected]>
> > (Put the word unsubscribe in the subject field)
> >
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email
> to:[email protected]<to%[email protected]>
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email 
> to:[email protected]<to%[email protected]>
> (Put the word unsubscribe in the subject field)
>



-- 
Tom Poisal, CET
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to