Dear Ron, Todd and Tom:

Appreciate so much your entries.

Yes, the warehouses (in planning stage) will be 40 feet high and they will 
store miscellaneous storage, Commodities I - IV.

If the 18% ceiling slope is a little bit above of the 16.7% established by 
NFPA13, a 30% design area increase will be necessary? If not, what else could I 
do? Ceiling false will go further of the client's budget.

Look forward to hearing from you.


Cesar Villavicencio




________________________________
From: Ron Greenman <[email protected]>
To: [email protected]
Sent: Sun, May 30, 2010 11:08:43 AM
Subject: Re: WAREHOUSE SLOPED CEILINGS

2 in 12 is considered flat. Over 2 in 12 is sloped, though, as Todd
points out, in Cesar's case it is minimal. I wish I could easily point
you to a head that has design data for sloped ceilings in warehouses
but you need to define your storage requirement and design approach a
bit more. If you're 12 feet or under with nothing outside the types
and classes of commodities (i.e.: nothing too out of the ordinary) a
head is probably available. If the building is still in the planning
stage perhaps you can get the architect to lower the slope (anything
between 2:12, minimum roof slope, and 3.5:12 will be a membrane of
some sort). There are directions for using standard spray sprinklers
in factories and warehouses with sawtooth roofs-anybody else here
remember the fifties-many of the buildings are still around. I cannot
believe there is no other solution than a costly and unnecessary
ceiling, I just don't work with storage enough to have a handy
solution in my pocket.

On Sun, May 30, 2010 at 7:58 AM, Todd Williams <[email protected]> wrote:
> A 16.7% slope is 2.0:12. and 18% slope is
> 2.16:12. The slope difference is 2" in 12 ft.
> That is pretty minimal. Could you get a Code mod
> for that? I would be tempted to go that route and
> over-design the system a little. I have no idea
> if the 2:12 was determined by testing and experience or was made up.
>
>
>
> At 10:38 AM 5/30/2010, you wrote:
>>Dear Forum Members,
>>
>>
>>NFPA 13 1999 chapter 7-3.1.3. says that
>>sprinkler system criteria is intended to apply
>>to buildings with ceiling slopes not exceeding 16.7 percent.
>>
>>What if we have warehouses with slopes of 18%,
>>what should I do? Should I ask a false ceiling
>>to the client? It is a lot of area, the client  will not be happy with this.
>>
>>Warehouses Class IV Commodities
>>
>>Could I make any adjustment in order to avoid
>>the construction of false ceiling?
>>
>>Please advise.
>>
>>Thanks so much.
>>
>>
>>
>>César Villavicencio
>>
>>
>>
>>_______________________________________________
>>Sprinklerforum mailing list
>>[email protected]
>>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>>For Technical Assistance, send an email to: [email protected]
>>
>>To Unsubscribe, send an email to:[email protected]
>>(Put the word unsubscribe in the subject field)
>
> Todd G. Williams, PE
> Fire Protection Design/Consulting
> Stonington, CT
> 860.535.2080
> www.fpdc.com
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering
Bates Technical College
Tacoma, WA

Member:
AFT WA 4184/AFL-CIO, SFPE, ASCET, NFPA, AFSA, NFSA AFAA, NIBS, WSAFM, WFC
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)



      
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to