thank you, So it has nothing to do with the gasket at all , correct?
On 6/4/2010 2:03 PM, [email protected] wrote: > The max end load is how much force the coupling can take by any force > attempting to pull it apart in the axial direction. That force could come > from internal pressure or from both internal pressure and weight of pipe > and contents below it, if in a vertical run. > > John Hoffman P.E. | Fire Protection Engineer | Facility Engineering > Services, KCP, LLC - Burns& McDonnell Engineering | National Nuclear > Security Administration's Kansas City Plant | Operated by Honeywell FM&T | > 2000 E. 95th St | Kansas City, MO 64131 | ph 816-997-7213 | > [email protected] > > > > From: Greg McGahan<[email protected]> > > To: [email protected] > > Date: 06/04/2010 02:30 PM > > Subject: max end load definition > > Sent by: [email protected] > > > > > > > > What does the "max end load" rating of a grooved coupling actually mean? > > Thanks, > Greg McGahan > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) > > > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) > _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)