Thanks Ron- you got me- I knew I should have said helium on its way to
becoming liquid helium on its way to NIST :)
What do you think about 'manual easily converted to automatic'?

-----Original Message-----
From: Ron Greenman [mailto:[email protected]] 
Sent: Monday, July 19, 2010 8:32 PM
To: [email protected]; [email protected]
Subject: Re: Finding leaks in a dry pipe system

Brad,

Boiling point of liquid helium 4 at one atmosphere: -268.95 C. Liquid
helium 3: -269.95 C.

On Mon, Jul 19, 2010 at 12:38 PM, Brad <[email protected]> wrote:
> Whooo! I thought maybe you were a half-way house for liquid helium on its
> way to NIST! Good luck with your problem- let us know how it turns out.
>
> -----Original Message-----
> From: David Bitton [mailto:[email protected]]
> Sent: Monday, July 19, 2010 2:17 PM
> To: [email protected]; [email protected]
> Subject: RE: Finding leaks in a dry pipe system
>
> I would like to clarify that the temperature in the freezer is -4, not
-40F.
> The character after the 4 was the degree sign, not a zero.  (Still a
pretty
> cold environment to be working in. That's also why any solution involving
> tripping the system and filling it with water is not practical.)
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Brad
> Sent: Monday, July 19, 2010 1:53 PM
> To: [email protected]
> Subject: RE: Finding leaks in a dry pipe system
>
> -40! (at that temp, C and F are the same). Wouldn't the fitter trying to
> find the leaks have to be wearing a ski-mask, ear muffs, goggles, etc--
> i.e., how do you hear, smell, see... or stick around for long? I guessed
at
> things like system size, CFM of air comp, etc. and it could happen that
the
> gage dropping could "look like a leak" for a couple hours until the whole
> thing reached 'steady state'. Who can think of better fire protection than
> keeping the combustible at -40? I do not question the need for sprinklers,
> but I think the 'sudden need for automatic sprinklers' is absurd. Would
> Manual easily converted to Automatic ever be considered by a committee?-
> (put a normally closed control valve on top of the dry valve)?
>
> -----Original Message-----
> From: tom poisal [mailto:[email protected]]
> Sent: Friday, July 16, 2010 9:38 PM
> To: [email protected]
> Subject: Re: Finding leaks in a dry pipe system
>
> would definitely rule out the air maintenance device, DPV trim, drum
drips,
> quick opening device and all that, if you haven't already done so.
>
> On Fri, Jul 16, 2010 at 8:25 PM, max brown
> <[email protected]>wrote:
>
>>
>> Have used high air pressures to add the advantage of hearing the leak
Also
>> have used the AQUA VELVA in compressor hose. Works as well as Ahmani but
>> cheaper. lol. Have had some sucess with both methods. Might try the high
>> tech Helium leak detector practice by professional leak detection company
>> but the air circulating , I assume complicates any method. Don't know of
a
>> reasonably priced liquid that freezes below -40; look for the drip. Maybe
> on
>> a Periodic Chemical chart there is an Element that would not freeze?
>>
>> > Date: Fri, 16 Jul 2010 12:36:46 -0700
>> > Subject: Re: Finding leaks in a dry pipe system
>> > From: [email protected]
>> > To: [email protected]
>> >
>> > Cold smoke like soldiers use for signaling. Pop a unit in the DPV,
>> > close it up, and then pressure it.
>> >
>> > On Fri, Jul 16, 2010 at 11:28 AM, David Bitton
>> > <[email protected]> wrote:
>> > > Thank you everyone for your replies.  We are still trying to find a
> way
>> to
>> > > locate the leaks without tripping the system and/or putting the
> freezer
>> out
>> > > of service.  (The aroma therapy sure is tempting...)  If that turns
> out
>> not
>> > > to be possible, we will explore the other methods.
>> > >
>> > > -----Original Message-----
>> > > From: [email protected]
>> > > [mailto:[email protected]] On Behalf Of Ben
>> Young
>> > > Sent: Friday, July 16, 2010 2:00 PM
>> > > To: [email protected]
>> > > Subject: Re: Finding leaks in a dry pipe system
>> > >
>> > > Frank Herrick gave a good way to find dry system leaks back in March,
>> > > actually.
>> > >
>> > >
>>
http://www.mail-archive.com/[email protected]/msg19989.html
>> > >
>> > >
>> > > Benjamin Young
>> > >
>> > >
>> > >
>> > > On Fri, Jul 16, 2010 at 1:26 PM, David Bitton
>> > > <[email protected]>wrote:
>> > >
>> > >> Yes, with the normal operating temperature at -4oF.  With regards to
>> the
>> > >> ultrasonic leak detectors, those that I have seen are limited to
>> operating
>> > >> temperatures above freezing.
>> > >>
>> > >> -----Original Message-----
>> > >> From: [email protected] [mailto:
>> > >> [email protected]] On Behalf Of
>> > >> [email protected]
>> > >> Sent: Friday, July 16, 2010 1:11 PM
>> > >> To: [email protected]
>> > >> Subject: Re: Finding leaks in a dry pipe system
>> > >>
>> > >> Is the freezer in service?
>> > >>
>> > >> LV
>> > >>
>> > >>
>> > >> ---- tom poisal <[email protected]> wrote:
>> > >> >  Buckets of soapy water and soft bush with plenty of helpers to go
>> over
>> > >> > every fitting, joint and weld.
>> > >> >
>> > >> > On Fri, Jul 16, 2010 at 12:18 PM, Matt Grise <[email protected]>
>> wrote:
>> > >> >
>> > >> > > There are leak detectors available that can detect the sound of
>> air
>> > >> leaking
>> > >> > > from pipes. They can often do better than ears.
>> > >> > >
>> > >> > > Matt Grisé PE*, LEED AP
>> > >> > > Sales Engineer
>> > >> > > Alliance Fire Protection
>> > >> > > *Licensed in KS & MO
>> > >> > >
>> > >> > > 913.888.0647 ph
>> > >> > > 913.888.0618 f
>> > >> > > 913.927.0222 cell
>> > >> > > www. AFPsprink.com
>> > >> > >
>> > >> > > -----Original Message-----
>> > >> > > From: [email protected] [mailto:
>> > >> > > [email protected]] On Behalf Of David
>> Bitton
>> > >> > > Sent: Friday, July 16, 2010 11:12 AM
>> > >> > > To: [email protected]
>> > >> > > Subject: Finding leaks in a dry pipe system
>> > >> > >
>> > >> > > Hello,
>> > >> > >
>> > >> > >
>> > >> > >
>> > >> > > I have a large cold storage freezer facility that is protected
by
>> > >> several
>> > >> > > dry pipe systems.  The systems are currently shut off due to
>> several
>> > >> leaks.
>> > >> > > A contractor used compressed air to pressurize the piping and
> find
>> > >> leaks,
>> > >> > > which he has repaired (mostly coming from the grooved
>> connections).
>> > >> > > However, there are additional leaks which has not been able to
>> find.
>> > >>  Is
>> > >> > > anyone aware of other methods of finding the leaks (other than
>> > >> compressed
>> > >> > > air)?
>> > >> > >
>> > >> > >
>> > >> > >
>> > >> > > Thanks,
>> > >> > >
>> > >> > >
>> > >> > >
>> > >> > > David Bitton, ing.
>> > >> > >
>> > >> > > Quest Loss Control Services Inc.
>> > >> > >
>> > >> > > Les services de prévention des sinistres Quest inc.
>> > >> > >
>> > >> > > 5100, rue de la Savane, bureau 200
>> > >> > >
>> > >> > > Montréal, QC H4P 1T8
>> > >> > >
>> > >> > > (514) 341-4545
>> > >> > >
>> > >> > > www.questlosscontrol.com
>> > >> > >
>> > >> > >
>> > >> > >
>> > >> > > _______________________________________________
>> > >> > > Sprinklerforum mailing list
>> > >> > > [email protected]
>> > >> > >
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>> > >> > >
>> > >> > > For Technical Assistance, send an email to:
>> [email protected]
>> > >> > >
>> > >> > > To Unsubscribe, send an email
>> > >>
>> > >
>
to:[email protected]<to%3asprinklerforum-requ...@fire
> sprinkler.org>
>> <to%3asprinklerforum-requ...@fire
>> > > sprinkler.org>
>> > >>
>> > >
>
<to%[email protected]<to%253ASprinklerforum-request
> @firesprinkler.org>
>> <to%253ASprinklerforum-request
>> > > @firesprinkler.org>
>> > >> >
>> > >> > > (Put the word unsubscribe in the subject field)
>> > >> > > _______________________________________________
>> > >> > > Sprinklerforum mailing list
>> > >> > > [email protected]
>> > >> > >
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>> > >> > >
>> > >> > > For Technical Assistance, send an email to:
>> [email protected]
>> > >> > >
>> > >> > > To Unsubscribe, send an email
>> > >>
>> > >
>
to:[email protected]<to%3asprinklerforum-requ...@fire
> sprinkler.org>
>> <to%3asprinklerforum-requ...@fire
>> > > sprinkler.org>
>> > >>
>> > >
>
<to%[email protected]<to%253ASprinklerforum-request
> @firesprinkler.org>
>> <to%253ASprinklerforum-request
>> > > @firesprinkler.org>
>> > >> >
>> > >> > > (Put the word unsubscribe in the subject field)
>> > >> > >
>> > >> >
>> > >> >
>> > >> >
>> > >> > --
>> > >> > Tom Poisal, CET
>> > >> > _______________________________________________
>> > >> > Sprinklerforum mailing list
>> > >> > [email protected]
>> > >> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>> > >> >
>> > >> > For Technical Assistance, send an email to:
>> [email protected]
>> > >> >
>> > >> > To Unsubscribe, send an email
>> > >>
>> > >
>
to:[email protected]<to%3asprinklerforum-requ...@fire
> sprinkler.org>
>> <to%3asprinklerforum-requ...@fire
>> > > sprinkler.org>
>> > >> > (Put the word unsubscribe in the subject field)
>> > >> _______________________________________________
>> > >> Sprinklerforum mailing list
>> > >> [email protected]
>> > >> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>> > >>
>> > >> For Technical Assistance, send an email to:
[email protected]
>> > >>
>> > >> To Unsubscribe, send an email
>> > >
>
to:[email protected]<to%3asprinklerforum-requ...@fire
> sprinkler.org>
>> <to%3asprinklerforum-requ...@fire
>> > > sprinkler.org>
>> > >> (Put the word unsubscribe in the subject field)
>> > >>
>> > >> _______________________________________________
>> > >> Sprinklerforum mailing list
>> > >> [email protected]
>> > >> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>> > >>
>> > >> For Technical Assistance, send an email to:
[email protected]
>> > >>
>> > >> To Unsubscribe, send an email
>> > >
>
to:[email protected]<to%3asprinklerforum-requ...@fire
> sprinkler.org>
>> <to%3asprinklerforum-requ...@fire
>> > > sprinkler.org>
>> > >> (Put the word unsubscribe in the subject field)
>> > >>
>> > > _______________________________________________
>> > > Sprinklerforum mailing list
>> > > [email protected]
>> > > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>> > >
>> > > For Technical Assistance, send an email to: [email protected]
>> > >
>> > > To Unsubscribe, send an email
>>
>
to:[email protected]<to%3asprinklerforum-requ...@fire
> sprinkler.org>
>> > > (Put the word unsubscribe in the subject field)
>> > >
>> > > _______________________________________________
>> > > Sprinklerforum mailing list
>> > > [email protected]
>> > > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>> > >
>> > > For Technical Assistance, send an email to: [email protected]
>> > >
>> > > To Unsubscribe, send an email
>>
>
to:[email protected]<to%3asprinklerforum-requ...@fire
> sprinkler.org>
>> > > (Put the word unsubscribe in the subject field)
>> > >
>> >
>> >
>> >
>> > --
>> > Ron Greenman
>> > Instructor
>> > Fire Protection Engineering
>> > Bates Technical College
>> > Tacoma, WA
>> >
>> > Member:
>> > AFT WA 4184/AFL-CIO, SFPE, ASCET, NFPA, AFSA, NFSA AFAA, NIBS, WSAFM,
> WFC
>> > _______________________________________________
>> > Sprinklerforum mailing list
>> > [email protected]
>> > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>> >
>> > For Technical Assistance, send an email to: [email protected]
>> >
>> > To Unsubscribe, send an email
>>
>
to:[email protected]<to%3asprinklerforum-requ...@fire
> sprinkler.org>
>> > (Put the word unsubscribe in the subject field)
>>
>> _________________________________________________________________
>> The New Busy is not the too busy. Combine all your e-mail accounts with
>> Hotmail.
>>
>>
>
http://www.windowslive.com/campaign/thenewbusy?tile=multiaccount&ocid=PID283
> 26::T:WLMTAGL:ON:WL:en-US:WM_HMP:042010_4
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email
>
to:[email protected]<to%3asprinklerforum-requ...@fire
> sprinkler.org>
>> (Put the word unsubscribe in the subject field)
>>
>
>
>
> --
> Tom Poisal, CET
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering
Bates Technical College
Tacoma, WA

Member:
AFT WA 4184/AFL-CIO, SFPE, ASCET, NFPA, AFSA, NFSA AFAA, NIBS, WSAFM, WFC

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to