Ed,

Measure on the slope.  See Figures 8.6.4.1.3.1(a) and (b) in the '10 
edition, and note the S dimension in the section.  It could be the L 
dimension if your branch lines are running perp to the slope.
-- 

PARSLEY CONSULTING

Ken Wagoner, SET

760.745.6181 voice

760.745.0537 fax

[email protected] <mailto:[email protected]> e-mail

www.ParsleyConsulting.com <http://www.ParsleyConsulting.com> website




Ed Kramer wrote:
> I think I know this, but need verification.  Minimum spacing between SSU's
> and SSP's is 6'.
>
> If installed on a sloped ceiling/roof, is the 6' a horizontal dimension, or
> is it measured along the slope?
>
>  
>
> Under a steeply sloped ceiling, it would be impossible to maintain 6'
> horizontally, so I assume the intent is to measure it along the slope.
>
> Comments, anyone?
>
>  
>
> Ed Kramer
>
> Littleton, CO
>