And there's the other third of the problem.

On Thu, Jul 22, 2010 at 11:49 AM, Steve Leyton
<[email protected]> wrote:
> I think it's prudent for the AHJ to request affirmation from the project 
> structural engineer that the proposed means of hanging and seismically 
> bracing fire sprinkler piping is within the design tolerances that were 
> calculated for the project.   In fact, in seminar environments, I encourage 
> AHJ's that if they have any doubts about whether applied loads can be borne 
> by building structure, that they should draw the SEOR into the mix prior to 
> approving the sprinkler design.  That said, it doesn't mean that the 
> sprinkler contractor becomes the structural engineer or has to do anything 
> more than provide the dead vertical and dynamic horizontal load values for 
> the hangers and bracing to the engineer, who should be able to efficiently 
> tell any interested party whether there is an issue or not.
>
> Same with the ceilings - I think it's a fair question.   It's also not a 
> question that I'm going to spend even three seconds considering the answer 
> to.   Pick up phone, call architect (or GC if I'm a sub making a deferred 
> submittal) and say, "Hello there.  I need a written statement from the 
> designer or design/build installer of the ceiling system that it conforms to 
> X, Y and Z."   NFPA 13 also calls out that ceilings used to support flexible 
> tube drops must meet certain threshold criteria and I'm sure as heck not 
> doing that certification either, but it's a valid request from the AHJ.
>
> When will sprinkler people stop taking ownership of stuff that isn't ours to 
> contend with?
>
> Steve Leyton
> Protection Design & Consulting
> San Diego, CA
>
>
>
>
> -----Original Message-----
> From: [email protected] 
> [mailto:[email protected]] On Behalf Of Chris Cahill
> Sent: Thursday, July 22, 2010 11:34 AM
> To: [email protected]
> Subject: RE: ASCE 7-05
>
> Got a little topic drift here...While I was/am in contracting for 6 years I
> spent the previous 9 as an AHJ.  So I sometimes am a little sympathetic to
> their side.  As AHJ I only had control over the one tiny issue of fire
> sprinklers.  The only thing I knew about the building was what the sprinkler
> contractor supplied.  There is something in the laundry list in 13 that
> requires the SC to provide all information necessary to make conditions
> clear.
>
> Looking back at the time I would have done exactly what George's AHJ did.
> (Today I'd do it a very little but different.) Just like I'd write the
> sprinkler is obstructed by a light or duct or whatever.  I probably even
> wrote to the effect move the sprinkler.  Contractors would complain why I
> didn't tell the electrician to move the light.  I sympathized but I had no
> authority over the electrician.  Nor did I have any idea what led to the
> conflict.  I also had no idea who these other trades were.  In the
> conversation all I could do was tell them I didn't care which solution, move
> light or sprinkler, that they had to take it up with the contractual chain
> of authority.  I'd supported them the best I could with the GC or Arch or
> Owner. Especially if it was a change to the EE or ME package thus was a
> legitimate CO for someone.  But if there were no changes or design build
> they were kinda on their own. Lack of coordination on DB wasn't something
> I'd stick my nose in then or now.
>
> Here's something for you AHJ's out there.  Now today if I went back to AHJ
> I'd still call the issue to the permit seeking sprinkler contractor BUT I'd
> change the language a bit.  I'd write the light, move the sprinkler or
> light.  On the structural issues I'd write to the sprinkler contractor to
> the effect it was their responsibility to pass along the issue to the
> GC...this was beyond the SC's scope and needs to be addressed by the
> structural PE.  If he forgot to consider 10" main it wasn't the SC's problem
> other than coordinating the paper trail to me the AHJ.
>
> On the ceiling issue George has, I'd write the SC to have the GC supply the
> require info.  But there would still be no permit until the issue was
> resolved.  I would probably require GC on the permit application and send
> the GC the same letter.
>
> In the end we are probably talking more semantics than anything else.
> Sending the letter written the right way and identifying the responsible
> party is an area the AHJ's can help the cause greatly.  Sadly, though I
> don't think may would follow the lead.
>
> Chris
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Ron Greenman
> Sent: Thursday, July 22, 2010 9:40 AM
> To: [email protected]
> Subject: Re: ASCE 7-05
>
> Yes and no Chris. For calcs we supply point loads and we should design
> to the point load strength of the structure so that hangers may need
> to be very close together relative to maximum. In seismic these truss
> systems typically require a brace on every third member. I can do this
> if I'm supplied with the numbers. The problem I'm railing against, and
> I may be at an extreme of my sensibility pendulum, is the AHJs
> requiring us to supply this info at a cost to us. We're a couple of
> sheets in a larger package and often the fire plan reviewer,
> particularly when a hired gun, only has our sheets and then demands
> that we provide info that may or may not be in the full submittal but
> is beyond our scope. Next you go to the GC (we're always too late in
> the game for my taste) and ask for info to comply with the AHJ and the
> GC tells us we have to do it. So pretty soon everybody, including the
> owner because it's obviously in his interest to not have to pay for
> it, is saying the requirement that the building hold up the pipe is in
> our book so our problem, and so the owner reaps a windfall profit on
> our backs. Same concept applies to the ceiling. Now some well placed
> verbiage in the contract specifically omitting the structural guys
> stuff from our scope is the best plan.
>
> On Thu, Jul 22, 2010 at 5:59 AM, Chris Cahill <[email protected]>
> wrote:
>> I agree with much of what you say Ron. But the AHJ has a point and an "if"
>> on the plan IMHO doesn't make it approvable. No offense to George but the
>> plan ain't done if he doesn't know how the ceiling is being seismically
>> treated.  The AHJ is just asking for which solution is being supplied.  If
>> return bends there could be hydraulic concerns over short drops and large
>> plates.
>>
>> Is this really different than indentifying the structural elements on the
>> sprinkler plan?  We certainly don't design the structure but we certainly
>> relay the information so the AHJ can agree we complied with spacing,
>> deflector height and obstructions.  And occasionally it's justified to
>> supply calculations showing the building will hold the sprinkler pipe.  We
>> don't do the calc's but they belong in our sprinkler package in these
> cases.
>>
>> Copy and paste the answers from the arch or ceiling guy, modify your plan
> as
>> necessary and you are done.
>>
>> Chris Cahill
>>
>> -----Original Message-----
>> From: [email protected]
>> [mailto:[email protected]] On Behalf Of Ron
> Greenman
>> Sent: Wednesday, July 21, 2010 8:55 PM
>> To: [email protected]
>> Subject: Re: ASCE 7-05
>>
>> George,
>>
>> Providing the information about the ceiling IS outside of your scope.
>> You only have to comply with the rules dependent on the ceiling
>> arrangement. Submittal drawings need only carry a note that to the
>> effect that if the ceiling is not seismically qualified then you will
>> comply with one of the two methods allowed per 13. Or just put the big
>> plate option on then tell the architect that that is what you intend
>> to do because you don't know about the seismic qualities of the
>> ceiling. I'll bet it takes no more than a couple of hours to get the
>> info of what the CEILING GUY intends to do and I'll bet he will intend
>> to brace the grid. This getting us to do all this leg work like making
>> sure the building will hold up the pipes is one of my pet peeves.
>> HELLO!!!! It's not my building. I don't have to put the pipes in, the
>> owner does. He just hired me to do it 'cause he can't/he's lazy/he's
>> got other stuff to do/etc. The pipes weigh what they weigh. I'll tell
>> him how much and I'll even tell him what the point loads will be and
>> find what I consider the best points of attachment to be. That's my
>> job. Whether the building is strong enough to deal with those forces
>> is his and his BUILDING DESIGNER's problem. I'm happy to coordinate
>> but it's HIS building. Same applies to the ceiling. I have enough of a
>> problem hitting center tile per the plans and then getting on site to
>> find that the layout has been turned 90 degrees or started from the
>> opposite end than was on that plan. As to what's meant by head
>> extension I've always read that to mean "drop" and not a "head
>> extender" per se.
>>
>> On Wed, Jul 21, 2010 at 12:57 PM, George Medina Jr <[email protected]>
> wrote:
>>>
>>> I have a plan checker requiring me to call out the required T-bar ceiling
>> grid construction in accordance with ASCE- 7-05 (Sec. 13.5.6.2.2 -
> 13.6.8.4)
>>  I do not have sections 13.3.1. & 13.3.2 which are referenced in the
>> aforementioned sections. Does anyone have code sections 13.3.1 & 13.3.2?
> The
>> fire sprinkler plan checker had sent me copies from there FPE who happens
> to
>> be on vacation for 2 weeks.
>>> I believe the t-bar ceiling call out is outside my scope of work, but
> upon
>> further reading There is a requirement for Fire Sprinkle Piping for being
> in
>> Seismic Zone 4. Section 13.5.6.2.2 (e.)
>>> States:
>>>  "Except where rigid braces are used to limit lateral deflections,
>> sprinkler heads and other penetrations shall have a 2" oversize ring,
>> sleeve, or adapter through the ceiling tile to allow for free movement of
> at
>> least 1 in. in all horizontal directions. Alternatively, a swing joint
> that
>> can accommodate 1 in. of ceiling movement in all horizontal directions is
>> permitted to be provided at the top of the sprinkler head extension" Does
>> head extension imply drop?
>>>
>>> How would I determine the Design Strength of Sections 13.6.8.3 - 3
>> (a.),(b.) & (c.)?
>>>
>>> I am not Familiar with these code sections, and if there is anyone with
>> experience in it, your guidance would greatly be appreciated.
>>>
>>> George Medina Jr.
>>>
>>> =
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>>
>>> For Technical Assistance, send an email to: [email protected]
>>>
>>> To Unsubscribe, send an email to:[email protected]
>>> (Put the word unsubscribe in the subject field)
>>>
>>
>>
>>
>> --
>> Ron Greenman
>> Instructor
>> Fire Protection Engineering
>> Bates Technical College
>> Tacoma, WA
>>
>> Member:
>> AFT WA 4184/AFL-CIO, SFPE, ASCET, NFPA, AFSA, NFSA AFAA, NIBS, WSAFM, WFC
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email to:[email protected]
>> (Put the word unsubscribe in the subject field)
>>
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email to:[email protected]
>> (Put the word unsubscribe in the subject field)
>>
>
>
>
> --
> Ron Greenman
> Instructor
> Fire Protection Engineering
> Bates Technical College
> Tacoma, WA
>
> Member:
> AFT WA 4184/AFL-CIO, SFPE, ASCET, NFPA, AFSA, NFSA AFAA, NIBS, WSAFM, WFC
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>
>
> __________ Information from ESET NOD32 Antivirus, version of virus signature 
> database 5302 (20100722) __________
>
> The message was checked by ESET NOD32 Antivirus.
>
> http://www.eset.com
>
>
>
> __________ Information from ESET NOD32 Antivirus, version of virus signature 
> database 5302 (20100722) __________
>
> The message was checked by ESET NOD32 Antivirus.
>
> http://www.eset.com
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering
Bates Technical College
Tacoma, WA

Member:
AFT WA 4184/AFL-CIO, SFPE, ASCET, NFPA, AFSA, NFSA AFAA, NIBS, WSAFM, WFC
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to