The Sprinkler Age magazine has an article about this with pictures of various 
options in last months edition. 

Forest Wilson
Cherokee Fire

Sent from my Verizon Wireless Phone

----- Reply message -----
From: "George Church" <[email protected]>
Date: Mon, Jul 26, 2010 11:27 am
Subject: Test connection for forward flow testing of backflow
To: <[email protected]>

you could simply leave a single FHV if that's suffieient for your flow; if
you start getting in to needing multiples, we'd stick a valved outlet on it
and when the test is performed, install a piece of 8" we have with 6- 2.5"
FHVs, run the test, take it home for the next time we need to flow a fire
pump installed "green" with a flowmeter/no header, or to measure the flow at
a preaction riser test valve when trip testing by connecting it to the test
tee above the valve. Its not like you use this thing very often- or as Reed
points out, like "never". 

glc

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Reed Roisum
Sent: Monday, July 26, 2010 10:38 AM
To: [email protected]; Charles Thurston
Subject: RE: Test connection for forward flow testing of backflow

What if you don't have a fire pump and the system demand is more than what
can be flowed out of the main drain (BTW, how do you measure the flow out of
the main drain?) We typically spec a 2 1/2" single outlet (size and # of
outlets dependent on the system demand), flush-type test connection with
male threads piped from the riser with a normally closed control valve.  Is
that what you are asking??


Reed A. Roisum, CET
Ulteig Engineers, Inc.




-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Charles
Thurston
Sent: Monday, July 26, 2010 9:29 AM
To: [email protected]
Subject: Re: Test connection for forward flow testing of backflow

Hello Craig,

Fire pump test header for sizes over 2", Otherwise the main drain

Monday, July 26, 2010, 8:31:34 AM, you wrote:

> Just trying to get a consensus,

> Got a backflow in a building at the riser location, what is the 
> preferred type of connection at the wall which would allow for forward
flow testing?

> Craig L. Prahl, CET
> Fire Protection Specialist
> Mechanical Department
> CH2MHILL
> Lockwood Greene
> 1500 International Drive
> Spartanburg, SC  29304-0491
> Direct - 864.599.4102
> Fax - 864.599.8439
> [email protected]
> http://www.ch2m.com
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

> For Technical Assistance, send an email to: [email protected]

> To Unsubscribe, send an email 
> to:[email protected]
> (Put the word unsubscribe in the subject field)



--
Best regards,
 Charles Thurston                            mailto:[email protected]
  Coastal Fire Protection/ Myrtle Beach Fire & Safety Group.
   AFAA Guest

Electronic Privacy Notice:
This e-mail, and any attachments, contains information that is, or may be,
covered by electronic communications privacy laws, and is also confidential
and proprietary in nature. If you are not the intended recipient, please be
advised that you are legally prohibited from retaining, using, copying,
distributing, or otherwise disclosing this information in any manner.
Instead, please reply to the sender that you have received this
communication in error, and then immediately delete it. Thank you in advance
for your cooperation

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to