Ron, I too have attached my response to the "check valve on standpipes" question from a couple of weeks ago. I have to agree with the esteemed Mr. Leyton, if we are going to take the time to write, you should be taking notes. Much love,
Cecil Bilbo Academy of Fire Sprinkler Technology Champaign, IL 217-363-2460 www.sprinkleracademy.com My nature sorts with my vocation, Francis Bacon is pretty sure that I am happy. Brad and Damien, The new requirement for the check valve tracks with the NFPA 14 committee's desire to see one there. they had good reasons, because any water left in a system is a good thing for a couple of reasons. One, it will allow SOEMTHING to come out if there is a fire while the system is closed. Second, you wouldn't have to fill every floor of the building if you drained the entire building (and you wouldn't have to close each floor's control valve. That is a good thing. And if you don't have to clase a valve on each floor, then you won't forget to open one either. The 13 Committee was offended that the NFPA 14 Committee was trying to place a check on the Sprinkler System. (Tongue in Cheek....) But they eventually relented and agreed. Some guy named Cecil ---------------------------------------- > Subject: RE: Check Valves in Combined Systems > Date: Mon, 2 Aug 2010 15:11:21 -0700 > From: [email protected] > To: [email protected] > > We did and I am reposting my reply below. It would be nice if you > would take the time to actually read what's being posted to the Forum > Ron; if I'm writing, you should be taking notes. > > "Section NFPA 14, 6.2.5.1 was revised in the 2003 ed. to require the > check valve in addition to a control valve for all sprinkler connections > to a standpipe." > > Steve Leyton > Protection Design & Consulting > Very busy here, very important stuff being done > > > -----Original Message----- > From: [email protected] > [mailto:[email protected]] On Behalf Of Ron > Greenman > Sent: Monday, August 02, 2010 2:55 PM > To: [email protected] > Subject: Check Valves in Combined Systems > > NFPA 14/2007 requires check valves and floor control valves on > combined standpipe/riser systems. Has this always been the case or was > this a new thing for 2007? Seems we discussed this a couple of weeks > ago. > > -- > Ron Greenman > Instructor > Fire Protection Engineering > Bates Technical College > 1101 So. Yakima Ave. > Tacoma, WA > > 253.680.7346 > > Member: > AFSA, SFPE, ASCET, NFPA, NFSA, AFAA, NIBS, WSAFM, WFC > > They are happy men whose natures sort with their vocations. -Francis > Bacon, essayist, philosopher, and statesman (1561-1626) > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email > to:[email protected] > (Put the word unsubscribe in the subject field) > > > __________ Information from ESET NOD32 Antivirus, version of virus > signature database 5335 (20100802) __________ > > The message was checked by ESET NOD32 Antivirus. > > http://www.eset.com > > > > __________ Information from ESET NOD32 Antivirus, version of virus > signature database 5335 (20100802) __________ > > The message was checked by ESET NOD32 Antivirus. > > http://www.eset.com > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) > _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)