I don't have a checklist, but I would like to point out that we as an
industry need to understand the quantum difference between a walkthrough
with the inspector/acceptance testing and what is a completely different
item, "Commissioning". 
>From NFPA 3 ROP Draft in NFPA's 2011 Annual Revision Cycle Report on
Proposals:

3.3.3.1* Commissioning (Cx). A systematic process that provides documented
confirmation that specific and interconnected fire and life safety systems
function according to the intended design criteria set forth in the project
documents and satisfy the owner's operational needs, including compliance
requirements of any applicable laws, regulations, codes, and standards
requiring fire and life safety systems

We've been working on this since December 2007, have two years till we're
thru -unless its handed back to us in 2012. There are over 40 of us on the
TC and we're on our 3rd staff liason! The above is the tip of the iceberg
and only addresses Commissioning, abbreviated Cx, from our point of view.
There's a whole industry that addresses Total Building Commissioning (TBC)
from the shell thru the lights and HVAC, telecom, and more. NIST asked NFPA
to produce the Fire Protection/Life Safety Component of this TBC and the
result is (will be?) NFPA 3, Recommended Practice on Commissioning and
Integrated Testing of Fire Protection and Life Safety Systems.   I've
presented seminars at AFSA and NFSA conventions twice on the topic, and
rather than be more complete in my response, I'll stop now. 

Go to www.nfpa.org, codes and standards, NFPA 3, the draft version is linked
there. There's 92 pages of proposals, our thoughts and actions, and the
current draft version of the Recommended Practice. 

Actually, I do have a form or checklist, see Annex C. If you're in a hurry,
don't bother looking, it isn't what you're looking for.

George Church
Rowe Sprinkler
Usual caveat that the above is only my opinion and it isn't adopted
anywhere, or even released, blah blah blah.

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
[email protected]
Sent: Thursday, August 19, 2010 4:52 PM
To: [email protected]
Subject: Final inspection co procedure

Question for AHJs:

Do you have available, and willing to share, a form or checklist you use
when conducting a walk through of a sprinkler system install/ commissioning.


If so, can you please send to me?
Thank you

Forest Wilson
Cherokee Fire

Sent from my Verizon Wireless Phone

----- Reply message -----
From: "Roland Huggins" <[email protected]>
Date: Thu, Aug 19, 2010 11:53 am
Subject: AFSA Alert - Antifreeze
To: <[email protected]>

I've always found it amusing that it changes within the chapter of the
standard.  It's been there a long time so we can only assume that two
different groups pulled the information together and that it was not
coordinated since it was not considered a significant issue (sounds better
than wasn't noticed and then after its published no one was squawking so no
need to change it).  The difference for PG is not very great but glycerin is
a different story.

Roland



On Aug 18, 2010, at 3:22 PM, Thom wrote:

> I find it interesting that NFPA uses 50% by Volume in the TIA yet uses 
> 50% by weight in the Handbooks and temp charts for GL.
> Any idea why this change in how it's measured?
> Thom
>

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to