I don't think heat trace would be approved for this use (at this point). I believe it is only for mains.

An enclosure may be the only alternative, not knowing the dimension of the units involved. It would just need to be an insulated box, since we are enclosing a furnace and residual heat would probably keep the space warm.

Sounds like a good pilot project.




At 10:46 AM 8/20/2010, you wrote:
You could use heat tracing. (...not a great idea, but it would work)

Matt Grisé PE*, LEED AP
Sales Engineer
Alliance Fire Protection
*Licensed in KS & MO

913.888.0647 ph
913.888.0618 f
913.927.0222 cell
www. AFPsprink.com


-----Original Message-----
From: [email protected] [mailto:[email protected]] On Behalf Of George Church
Sent: Friday, August 20, 2010 9:45 AM
To: [email protected]
Subject: 13D attic Fuel-fired protection

In those areas with cold weather and 13D in place, has anyone come up with a
resolution for protecting a head above the fuel fired furnace in an
unconditioned attic space short of walling it off so a wet pipe could be
safe?
We certainly want to minimize the impact at this critical time in our IRC
mandate here in PA, so that we can provide the builders and homeowners with
an affordable, smooth transition to a sprinklered Commonwealth.

Losing AF is quite a blow, even if its temporary (I hope!) for areas where
50-50 works. It'd take a really tall dry upright, past the listing
limitation.

From: George Church [mailto:[email protected]]
Sent: Friday, August 20, 2010 10:39 AM
To: 'Tim Knisely'
Subject: RE: Sprinkler question...

Without antifreeze, its seal it in and pop a wet head in it, or install a
tiny dry system. I'm confident that the additional testing will soon allow
premix 50-50 solutions and we'll be back to a small AF loop for a head in
the attic atop the unit.
I would argue passionately that sticking a furnace in an attic does NOT make
the space conditioned sufficiently for a wet pipe to survive a winter around
here.

Tyco now has a CPVC dry system and residential dry pendents, but that's a
huge expense for a single head. Even an AF loop with the RPZ and associated
backflow and fluid maintenance chores introduces too much complexity for 13D
IMHO.
We should be thinking of these as Install and Forget- because that is what
will happen.

Will check around- I'm posting this to the AFSA Sprinkler Forum to see if
anyone has additional thoughts.

George Church'
Rowe Sprinkler
[email protected]
570-837-7647
From: Tim Knisely [mailto:[email protected]]
Sent: Friday, August 20, 2010 8:46 AM
To: 'George L. Church Jr.'
Subject: Sprinkler question...

George,

With sprinklers now required in unfinished attics where a fuel-fired
appliance is located, what is the preferred method to keep this from
freezing?  I've heard some people say that the space is now heated and the
head won't freeze.  But, I'm not sure if some of the newer high-efficiency
furnaces put off that much heat.  One option is to frame in a room to
capture the heat, but curious to see what some others might be.

Thanks.

Tim E. Knisely, Senior Fire Inspector
Centre Region Code Administration
2643 Gateway Drive, Suite #2
State College, PA  16801
(814) 231-3058
(814) 231-3088 Fax
E-mail: [email protected]


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to