So if it is a wall, what is the T-rating question? NFPA 101 does not require a T-rating, only a 1-hour F-rating.
Some firestops can give you a T-rating with metallic pipe by using a wrap strip or other device, but usually it is only a 1/2 hour or sometimes 3/4 hour rating. . There may be a 1-hour T-rated firestop with metal pipe penetrant out there but how to find it. If you end up having to provide one the best bet is to contact a firestop mfr and see what they can provide. John Hoffman P.E. | Fire Protection Engineer | Facility Engineering Services, KCP, LLC - Burns & McDonnell Engineering | National Nuclear Security Administration's Kansas City Plant | Operated by Honeywell FM&T | 2000 E. 95th St | Kansas City, MO 64131 | ph 816-997-7213 | [email protected] From: "Brown, Mike" <[email protected]> To: "[email protected]" <[email protected]> Date: 09/01/2010 10:37 AM Subject: RE: T-Rating of Fire stop Sent by: [email protected] It is a wall. Mike Brown Project Designer Sunland Fire Protection, Inc. 1218 Elon Place High Point, NC 27263 [email protected] Business: 336-886-7027 Ext. #140 Fax: 336-886-7024 -----Original Message----- From: [email protected] [ mailto:[email protected]] On Behalf Of [email protected] Sent: Wednesday, September 01, 2010 11:29 AM To: [email protected] Subject: Re: T-Rating of Fire stop NFPA 101 only requires a 1-hour T-rating in a fire-rated horizontal assembly. There aren't that many places that utilize fire-rated horizontal assemblies. Is that what you are penetrating? Don't need the T-rating for a regular fire-rated floor if the pipe is not in direct contact with combustibles. See 8.3.5.1.4 of NFPA 101 2009 edition. John Hoffman P.E. | Fire Protection Engineer | Facility Engineering Services, KCP, LLC - Burns & McDonnell Engineering | National Nuclear Security Administration's Kansas City Plant | Operated by Honeywell FM&T | 2000 E. 95th St | Kansas City, MO 64131 | ph 816-997-7213 | [email protected] From: "Brown, Mike" <[email protected]> To: "[email protected]" <[email protected]> Date: 09/01/2010 10:03 AM Subject: T-Rating of Fire stop Sent by: [email protected] We have a project that our fire stop T-rating is in question. (Gov't project) They referenced the UFC 2-1.1 which then sends you to NFPA 101. Basically we need a T-rating of 1 hour. Has anyone had this before if so....which brand fire stop did you use? Mike Brown Project Designer Sunland Fire Protection, Inc. 1218 Elon Place High Point, NC 27263 [email protected] Business: 336-886-7027 Ext. #140 Fax: 336-886-7024 _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)