NFPA 13 and 20 certainly DO allow performance-based designs under 1.5
Equivalency. 
So long as a test indicates a certain level of performance, and the AHJ
approves the use of those results and the contractor is prudent enough to
allow degradation of pump and water supply to the satisfaction of the AHJ,
or AHJs (plural) since BCO, fire official, and insurance AHJ could all be
involved, if it is APPROVED (found acceptable to the AHJs) then there is
nothing preventing the use of more than the rating of a pump if that higher
level of performance exists that I'm aware of. Written documentation by a
qualified person must be submitted to the AHJ to gain approval.

Versus the competitor who, in a proposal I just read, that their insurance
carrier wouldn't let them do anything that wasn't in the code. Well, its in
there, I just don't think they know what options are available to them, and
I sure bet they don't subscribe to this Forum where they could learn. You
get out of it what you put into it, and from the sound of their proposal,
they don't put forth much extra effort. (sigh) sometimes its like shooting
fish in a barrel, we got the job. Thanks, AFSA, for hosting the Forum.

glc 

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
[email protected]
Sent: Wednesday, September 01, 2010 11:42 AM
To: Fletcher, Ron; [email protected]
Subject: Re: Diesel Pump Engine RPM

The pumps are listed by UL per an approved, ISO registered process. 

The mfr wont guarantee a new pump to perform up to and including the safety
margin. 

You are proposing a performance based design, using the safety margin. 

If this is not an accepted design method in new pump installations, then it
is likely not in retro fits either. 

The pump performance test could be used to measure any degradation in
performance against the original curve. 


Forest Wilson
Cherokee Fire
Sent from my Verizon Wireless Phone

----- Reply message -----
From: "Fletcher, Ron" <[email protected]>
Date: Wed, Sep 1, 2010 9:58 am
Subject: Diesel Pump Engine RPM
To: <[email protected]>

For a retrofit you wouldn't do a pump test and then use the results of the
test for the calculations?


Ron Fletcher
Aero Automatic
Phoenix, AZ



-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of
[email protected]
Sent: Tuesday, August 31, 2010 6:50 PM
To: [email protected]
Subject: Re: Diesel Pump Engine RPM

I would contact the mfr. The listing is based on their data sheets i
believe. So the calcs are based on the listed, approved pump. 

Forest

Sent from my Verizon Wireless Phone

Sent from my Verizon Wireless Phone

----- Reply message -----
From: "Tom Duross" <[email protected]>
Date: Tue, Aug 31, 2010 8:09 pm
Subject: Diesel Pump Engine RPM
To: <[email protected]>

Short answer, yes I believe.
Typically, engine speed required by the pump is at 150% and climbs according
to the engine as you approach no load.  Engines have an operating range and
usually selected and governor set for the pump's requirements.  I thought
there might be a disclaimer in the most recent 20 regarding PLD controllers,
but not to my knowledge.  I know with non-PLD controllers, we always start
at 150% and work our way back when testing engine-driven pumps as that helps
cool-down.  Plus, you can check RPM at first flow point.  It's unfortunate
affinity calculations are based upon constant speed (as I understand them),
which never exists regardless of driver type.
Sorry for seeming vague but the books beyond arms reach.
TD


NFPA #20, 2003, 11.2.4.1.1. "Engines shall be provided with a governor
capable of regulating engine speed within a range of 10 percent between
shutoff and maximum load condition of the pump."

Does this mean that a 1760 rpm rated engine running at 1860 rpm is
acceptable?

If a 1760 rpm rated pump when tested produced 1860 rpm (less than 10%) can
the pressure produced at the higher rpm be used for the system calculations?
In other words can the actual pump test be used for the system calc's or
must we use the manufacturers data sheet regardless the test results?

The pump is a PLD if that matters.

Ron Fletcher

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)


_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to