All requirements for anti-backflow protection start with the plumbing
code. Who administers and enforces that code or portion thereof is up
to local legislation but typically the plumbing official and the water
purveyor. The requirement for forward flow testing of anti-backflow
devices in NFPA 25 is the only "shall" reference to those devices I'm
aware of in any of the NFPA codes or standards.

On Mon, Sep 13, 2010 at 2:11 PM, Brian Harris
<[email protected]> wrote:
> Thanks for all the info regarding RPZ's and antifreeze systems. One more
> question, the requirement of RPZ's on systems with fire pumps, is this from
> the water authority as well?
>
>
>
> Brian Harris
>
> Design Manager
>
> First Defense Fire Protection
>
> 11957 Ramah Church Road
>
> Huntersville, NC 28078
>
> Phone: 704.948.3506
>
> Fax: 704.948.3507
>
> Nicet # 128476
>
>
>
>
>
>
>
> =======
> Email scanned by PC Tools - No viruses or spyware found.
> (Email Guard: 7.0.0.21, Virus/Spyware Database: 6.15860)
> http://www.pctools.com/
> =======
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
AFSA, SFPE, ASCET, NFPA, NFSA, AFAA, ASEE, NIBS, WSAFM, WFC

They are happy men whose natures sort with their vocations. -Francis
Bacon, essayist, philosopher, and statesman (1561-1626)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to