Jack,
The hydraulic summary sheet from the calcs has always sufficed for our submittals. This, of course, combined with the required NFPA 13 list of what should be on the drawings. I have asked several AHJs about this and they have no idea what it is either. If you happen to come across one....please shoot me a copy. The UCC checklist in question also lists a 10 psi safety factor on all hydraulic calculations. I've asked AHJs to show me where in the Uniform Construction Code and the NFPA standards that this is a requirement. No one has given me an answer yet. I only know of one jurisdiction around the Harrisburg area that has a legally adopted amendment. Best Regards, Ken Holsopple Rowe Sprinkler Systems Inc. _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)