11.1.2 requires the more demanding "design" to extend 15' beyond the hazard
but does not say that the actual protection can stop at that point.  Unless
the space above the office ceiling can be considered "concealed", I don't
see any way around full coverage.

Tony Liddic, CET
MRH Sprinkler Design LLC
356 Laurel Glen Dr.
Springboro, OH  45066
937-369-7926
http://www.mrhsprinklerdesign.com
[email protected]


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of George Medina
Jr
Sent: Friday, October 08, 2010 12:07 PM
To: [email protected]
Subject: Re: Full height walls in exposed room

NFPA-13 (2007ed.) Sec. 11.1.2 and A.11.1.2 might help.


George Medina Jr. 
Sr. Fire Sprinkler Designer 



-----Original Message-----
From: Dewayne Martinez <[email protected]>
To: [email protected]
Sent: Fri, Oct 8, 2010 8:00 am
Subject: Full height walls in exposed room


Office with ceilings containing a storage room with no ceiling.  I told he
architect that the walls for this room would have to go full height r else
we would need to add sprinklers in the non-combustible space bove the
office.  He is looking for a specific code reference....is here?  For the
full height wall, would it require gyp bd on one side nly or both sides with
all the gaps filled?
hanks,

ewayne
______________________________________________
prinklerforum mailing list
[email protected]
ttp://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected] To
Unsubscribe, send an email to:[email protected]
Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to