Just a question. Do all hanger materials need to be listed or do
certain types fall under that typically used category like some of the
common pipe types? I ask because those split types were very common
for a long, long time.

On Tue, Oct 12, 2010 at 7:47 AM, ParsleyConsulting
<[email protected]> wrote:
>  Thomas,
>
> Figure A.9.1.1 in the '10 edition of -13 clearly shows a "split ring" hanger
> as a type of an "acceptable hanger", so my first thought is that if the
> rings themselves were listed, as they were required to be, you met the
> criteria established by the standard.
>
> A quick look at two manufacturers catalog data showed neither had a listed
> split ring.
>
> Just my thoughts.
> --
> PARSLEY CONSULTING
> Ken Wagoner, SET
> 760.745.6181 voice
> 760.745.0537 fax
> [email protected] <mailto:[email protected]> e-mail
> www.ParsleyConsulting.com <http://www.ParsleyConsulting.com> website
>
>
> IMPORTANT NOTICE: This correspondence is not a Formal Interpretation issued
> pursuant to NFPA Regulations. Any opinion expressed is the personal opinion
> of the author and does not necessarily represent the official position of
> the NFPA or its Technical Committees. In addition, this correspondence is
> neither intended, nor should it be relied upon, to provide professional
> consultation or services.
>
>
>  10/12/2010 6:30 AM, Thomas Watt wrote:
>>
>>   I was driving down the highway the other day when I passed a job I did
>> about 4 or 5 years ago, a dry system (4"main w/2" branch lines) over a
>> covered play area outside an elementary school. I had some reservations at
>> the time but was told to follow the plan with the materials provided. What
>> I
>> was concerned with at the time was installing Sammy screws vertically into
>> boxed steel beams with no way to reach a back nut to install it. I had to
>> drill pilot holes and oil the threads to help keep the Sammys from
>> breaking
>> off.
>>    The other problem I did not realize at the time but have become aware
>> of
>> through my parasitic leaching from this remakably informative discussion
>> group. Other than the 4" rings on the main, all of the hangers are the
>> split-ring type. I remember reading here that they do not meet the
>> requirements of NFPA 13 for hanging pipe.
>>    Call me paranoid but I think that this system could fall given the
>> right
>> set of circumstances. Remember, this system hangs above small children at
>> play. Am I  obligated to inform the AHJ or some other entity?
>>
>> Thomas Watt
>> A parasite/fitter/foreman (laid-off again)
>> Orlando, Florida
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email to:[email protected]
>> (Put the word unsubscribe in the subject field)
>>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
AFSA, SFPE, ASCET, NFPA, NFSA, AFAA, ASEE, NIBS, WSAFM, WFC

They are happy men whose natures sort with their vocations. -Francis
Bacon, essayist, philosopher, and statesman (1561-1626)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to