Agreed. I also was referring to SSU & SSP. You can apply Obstructed
Construction Rules per the type of sprinkler used.

 

Bobby Gillett

Sr. Project Manager

Key Fire Protection, Inc.

(731) 424-0130 office  (731) 424-9285 fax 

(731) 267-4853 cell

 <mailto:[email protected]>
[email protected]

 

 

  _____  

From: [email protected]
[mailto:[email protected]] On Behalf Of Brad
Casterline
Sent: Monday, October 25, 2010 2:00 PM
To: [email protected]
Subject: RE: Maximum Deflector Distance below Z Purlins

 

If the purlin spacing does not exceed 7'-6", I think so.

-----Original Message-----
From: Bobby Gillett [mailto:[email protected]]
Sent: Monday, October 25, 2010 1:53 PM
To: [email protected]
Subject: RE: Maximum Deflector Distance below Z Purlins

If my understanding is correct, this is considered obstructed construction
now so it would be per 8.6.4.1.2 and if the scenario is typical to most
purlin buildings you should be able to utilize 8.6.4.1.2 (1) 1"-6". What say
everyone else?



Bobby Gillett

Sr. Project Manager

Key Fire Protection, Inc.

(731) 424-0130 office  (731) 424-9285 fax

(731) 267-4853 cell

 <mailto:[email protected]>
[email protected]





  _____ 

From: [email protected]
[mailto:[email protected]] On Behalf Of Mike
Hairfield
Sent: Monday, October 25, 2010 1:44 PM
To: AFSA SprinklerFORUM
Subject: Maximum Deflector Distance below Z Purlins





OK Metal building with 9 1/2" Z-Purlins, what is maximum distance that the
deflector can be below the
bottom of the Purlin.

Mike                                    
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

  _____ 

No virus found in this message.
Checked by AVG - www.avg.com
Version: 10.0.1152 / Virus Database: 422/3218 - Release Date: 10/25/10

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

  _____  

No virus found in this message.
Checked by AVG - www.avg.com
Version: 10.0.1152 / Virus Database: 422/3218 - Release Date: 10/25/10

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to