During a 13 TC meeting on just this topic, the FM guy (at that time - Joe Hankins) stated that FM had tested mixed commodities and you definitely had to assign the actual height of storage for the higher hazard even when the upper portions were a lower hazard. The fire was far worse than a one would see for the higher hazard at its lower height.

The idea by Chris to segregate with in-rack sprinklers (insert at EVERY flue) is a defendable equivalency approach.

Roland

On Nov 3, 2010, at 12:13 PM, Matt Grise wrote:

Right now I am leaning towards the FM guidelines they do have some options for getting it done without in-racks.

Matt Grisé PE*, LEED AP
Sales Engineer
Alliance Fire Protection
*Licensed in KS & MO

913.888.0647 ph
913.888.0618 f
913.927.0222 cell
www. AFPsprink.com