I'd say it depends.  If it was in full compliance with the Code before you
add sprinklers I'd say no the sprinklers are above and beyond the MINIMUM of
the Code.

If it was not in compliance then maybe.  I'd say it needs to be brought up
to Code in all respects.  Some scenarios require both sprinklers and smoke
control, others just sprinklers.

Look in Chapter 1 for applicability that I believe is what is the guiding
Code section.  If it is existing HPS and doesn't have smoke control I'd be
first guessing it was not in compliance when built (or changed to HPS). 

Chris Cahill    


-----Original Message-----
From: Matt Grise [mailto:[email protected]] 
Sent: Thursday, November 04, 2010 2:53 PM
To: '[email protected]'
Subject: smoke vents for retrofit

If an existing building is retrofit with an area/density system to protect
high piled storage, does it need to have smoke vents and draft curtains
added as described in the IFC, or is that just new construction?

I looked around in the IFC/IBC/IEBC books, but I could not find anything
that would exempt the vents and curtains. Does anyone recall any way to
avoid them (other than ESFR)?