Carbon steel: expansion = 6.7 x 10^-6 x L. x delta T.
Example: 200 feet of steel pipe installed at 30 degrees F and raised to 100
degrees F.
6.7 x 10^-6 x 200ft x 12in/ft x 70degrees = 1.13 inches
Copper: 9.3 x 10^-6
The source, Perry's Engineering Manual, puts a range on that coefficient of 32
to 212 degrees F. For down and dirty purposes, this should work to foreseeable
colder temps.
Dave
David A. de Vries, P.E., CSP
Firetech Engineering Incorporated
--- On Wed, 11/10/10, Charles Thurston <[email protected]> wrote:
From: Charles Thurston <[email protected]>
Subject: Pipe Expansion
To: "sprinklerforum" <[email protected]>
Date: Wednesday, November 10, 2010, 8:10 AM
Hello sprinklerforum,
Does anybody know of a down and dirty chart or calculator to figure pipe
expansion lengths due to temperature change ?
--
Best regards,
Charles Thurston mailto:[email protected]
Coastal Fire Protection/ Myrtle Beach Fire & Safety Group.
AFAA Guest
Electronic Privacy Notice:
This e-mail, and any attachments, contains information that is, or may
be, covered by electronic communications privacy laws, and is also
confidential and proprietary in nature. If you are not the intended
recipient, please be advised that you are legally prohibited from
retaining, using, copying, distributing, or otherwise disclosing this
information in any manner. Instead, please reply to the sender that
you have received this communication in error, and then immediately
delete it. Thank you in advance for your cooperation
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]
To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]
To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)