Btw, last time I tried to do more than spot the dots then connect the dots I
got it wrong, even after I said I corrected it- turns out 1.5 trees, so 4
heads in that closet would have gotten back to the original 6!!! (and no
obstructed head problem with the inspector)

Brad Casterline, NICET IV
Project Manager – Fire Protection
 
FSC, Inc.
P: 913-722-3473
D: 816-841-8732
[email protected]
www.fsc-inc.com
 
Engineering Solutions for the Built Environment
 

-----Original Message-----
From: Brad Casterline [mailto:[email protected]] 
Sent: Friday, November 12, 2010 4:06 PM
To: [email protected]
Subject: RE: Omitting sprinklers in a high building

10 MW fire!= 10,000 KJ/sec. If a big dry xmas tree was a 22 pound block of
oven dried douglas fir with heat of combustion of 20 MJ/Kg, this means 20
big dry xmas trees, right? What if you stood them on top of each other? :)
 
-----Original Message-----
From: Chris Cahill [mailto:[email protected]] 
Sent: Friday, November 12, 2010 3:42 PM
To: [email protected]
Subject: RE: Omitting sprinklers in a high building

Effective at 50' in what occupancy?  Storage to 45' sure, convention set up
maybe, light hazard atrium, maybe not.  Of course we'd probably need to
start with what is 'effective'. With a square function there is a BIG
difference between 50' and 119' in the heat at the roof to even make them go
off.  That is not to say they are not required by code as they are no matter
what height (with others referenced exceptions). But a good FPE and
reasonable AHJ you MIGHT be able omit.  Your competition is suspect with a
blanket statement to the effect.  If they go with the competition make sure
the customer enforces the contract and no extras for the roof.  Bet they
change their tune.  

As AHJ back in '99 I agreed with omitting the sprinklers at the roof in the
NHL Wild arena.  Can't recall the exact height but it's in the 150' range.
We burned a 10 MW fire in the old arena and at 100' it was very doubtful the
sprinklers would operate.  We had instrumentation.  The design fires we set
at 10 MW when occupied on the upper levels and larger if no one above the
main concourse.  For the boat shows we acknowledged larger fires were
possible BUT the size of the ice (fuel area), very infrequent events, large
paid FD and fire prevention personal from the FD on site when open to the
public were mitigating factors.  There are also an array of beam smoke
detectors to help with early detection. Remember this was pre FDS days.  10
years later I'd still stand behind the concept.  

Chris Cahill   

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Matt Grise
Sent: Friday, November 12, 2010 11:49 AM
To: '[email protected]'
Subject: RE: Omitting sprinklers in a high building

Just saw this again today.

NFPA 13-2010 A.8.1.1 This standard contemplates full sprinkler protection
for all areas including walk-in coolers, freezers, bank vaults, and similar
areas. Other NFPA standards that mandate sprinkler installation might not
require sprinklers in certain areas. Based upon experience and testing,
sprinklers have been found to be effective and necessary at heights in
excess of 50 ft (15.2 m). For a building to meet the intended level of
protection afforded by NFPA 13, sprinklers must not be omitted from such
high ceiling spaces.
The requirements of this standard should be used insofar as they are
applicable. The authority having jurisdiction should be consulted in each
case. A building is considered sprinklered throughout when protected in
accordance with the requirements of this standard.

Matt Grisé PE*, LEED AP 
Sales Engineer 
Alliance Fire Protection 
*Licensed in KS & MO 

913.888.0647 ph 
913.888.0618 f 
913.927.0222 cell 
www. AFPsprink.com 


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Dewayne
Martinez
Sent: Friday, November 12, 2010 11:47 AM
To: [email protected]
Subject: Omitting sprinklers in a high building

Is there anywhere in NFPA 13 stating that you can omit sprinklers if the
roof structure is above a certain height above the ground?
We have a manufacturing building that will have a 119ft deck and my
competition is stating that sprinklers would not be required.
 
Thanks,
Dewayne
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to