Steve,
I think the language in the 2010 edition of NFPA-13 addresses your concerns:
12.1.1.2 Early suppression fast-response (ESFR) sprinklers
shall not be used in buildings with automatic heat or smoke
vents unless the vents use a high-temperature rated, standard response
operating mechanism
Hope that's in reference to your situation.
PARSLEY CONSULTING
Ken Wagoner, SET
760.745.6181 voice
760.745.0537 fax
[email protected] <mailto:[email protected]>e-mail
www.ParsleyConsulting.com <http://www.ParsleyConsulting.com>website
On 11/15/2010 3:15 PM, Smith, Steven D. (CSFD) wrote:
So the lack of any such wording (sprinkler may/may not be used in bldgs
with vents) in the mfg's installation instructions mean it's
permissible?
-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Forest
Wilson
Sent: Monday, November 15, 2010 3:34 PM
To: [email protected]
Subject: Re: Sprinkler Listing Question
Everything must be installed in accordance with manufacturers
instructions, they are listed to be used in compliance with mfr
instructions
On 11/15/2010 5:23 PM, Smith, Steven D. (CSFD) wrote:
I guess more information is warranted.
ESFR sprinklers. If they are installed in warehouses with vents, does
that void their listing? It is my understanding that they were
tested/listed without vents present.
PS- I am aware of the footnote for Table 2306.2 of the IFC. :-)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]
To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
For Technical Assistance, send an email to: [email protected]
To Unsubscribe, send an email to:[email protected]