For the refractometer I just use a Brix scale and calibrate it by
mixing up the solution I should have and comparing it to the solution
I do have. Accuracy of the scale then is irrelevant.

On Tue, Nov 16, 2010 at 12:28 PM, Chris Cahill <[email protected]> wrote:
> If you are trying to prevent the pipe from breaking there is some safety in
> the difference between freeze point and break point of the AF.  We usually
> speak in terms of freeze point but the breaking point is much lower.
> Between the two points my limited kitchen research shows a milkshake
> consistency. If you use the ASHRAE data you are probably fine with no SD.
> Our friend Scott F. believes we should be using the coldest ever recorded
> for that area. ASHRAE, coldest ever or some SD plus or not a further safety
> (8) all have merit but I don't think there is any specific guidance.  I
> thought I read ASHRAE once but have been unable to find a reference.  There
> is also some safety potentially in the location of the piping, in how long
> it is exposed to a specific cold temp and the time it takes to cool the pipe
> to ambient.  Think in an residential attic, the outside ambient a few
> degrees below the temp it's rated for and a couple hours vs. an exterior
> canopy on the north side, exposed piping, a windy day and 20 degrees below
> the rated point for 8 hours.
>
> The 40 IMHO may be related to the fact to keep something at 40 the HVAC
> units will be putting out something less than 40 and could cause a local
> problem.  Yeah it doesn't explain an outside reasoning.
>
> If you are interested in the ability of cold AF to fight a fire I think
> there is a gaping hole in the information available. I know 13 went all DW
> on us for bigger systems but that was a knee-jerk reaction not unlike IMHO
> the current TIA.  And DW doesn't tell us anything about the character of the
> spray of AF at cold temps or how long it takes the AF to clear.  Something
> needs to be done but we don't really know what yet. In theory we might want
> to walk a closer line on the rated temp vs. potential ambient to preserve
> some more firefighting ability or maybe not depending on the flow
> characteristics, size of the flow path and increased fire contribution of
> the AF.
>
> Pocket refractometers - I have my doubts especially when used in the field
> after bouncing around a truck for years.
>
> I doubt many use pre-mix.  At best a few do for the original installation
> but not on annuals if it needs a little touching up.
>
> Chris Cahill
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of David de
> Vries
> Sent: Tuesday, November 16, 2010 1:35 PM
> To: AFSA SprinklerForum
> Subject: Anti-Freeze Solution Freeze Point
>
> Is there any guidance on how much of a safety factor an anti-freeze solution
> should have?  I cannot find any such in 13, but of course 13 requires an 8
> degree F cushion for wet systems (maintain at or above 40 F).
>
> Looking at the ASHRAE Handbook there is weather data which shows the mean
> coldest temp and a standard deviation for locations throughout the USA and
> Canada.  Using that data, what should be the design basis, i.e. how many
> standard deviations below the mean coldest temp?
>
> Does it make sense for a locale with a reported mean coldest temp of -10 and
> 5.8 standard deviation to design for 2 standard deviations below and a
> safety factor?  So, freeze point of anti-freeze solution = -10 - 2(5.8) -8 =
> -30 F or lower?
>
> How accurate are the pocket refractometers used in the field?
>
> Do most contractors use pre-mixed anti-freeze solutions?
>
> As always, the Forum's insights are welcome.
>
> Dave
>
> David A. de Vries, P.E., CSP
> Firetech Engineering Incorporated
>
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
AFSA, SFPE, ASCET, NFPA, NFSA, AFAA, ASEE, NIBS, WSAFM, WFC

They are happy men whose natures sort with their vocations. -Francis
Bacon, essayist, philosopher, and statesman (1561-1626)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to