First, take a look at the new (2010) NFPA 13 8.15.1.2.11 and
A.8.15.1.2.11 and the handbook commentary to A.8.15.1.2.11.  Then check
out their website information and UL site info on the specific product
they are using.
I've got an inspection to run to but they were just at the SC Fire
Academy yesterday educating folks on their products.  Note that they
have multiple related products.  Some are intumescent coatings, some
soak in, some are clear, some are opaque, etc.

Their website is:
http://noburn.com/ 

Their SE office number is 352.404.4274 in case you want to call & get
the number for representatives for the CA area.
 

David W. S. Blackwell, II, PE, CFI-I, CFPE
Engineering 
---------------------------------------------------------------- 
Office of State Fire Marshal 
141 Monticello Trail 
Columbia, SC 29203 
Phone:  803.896.9833 
Fax:  803.896.9806 
Email:  [email protected] 
OSFM Website: http://www.llr.state.sc.us/firemarshal.asp 
---------------------------------------------------------------- 


-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of A.P.Silva
Sent: Friday, November 19, 2010 1:23 AM
To: [email protected]
Subject: Fire retardant coating

I'm checking out a fire retardant coating called 'noburn'. Has anyone
come
across it? In particular, has it been used to omit sprinklers in a
combustible concealed space?

NFPA 13, 2007 section 8.15.1.2.10: Concealed spaces where rigid
materials
are used and the exposed surfaces have a flame spread index of 25 or
less,
and the materials have been demonstrated not to propogate fire when
tested
in accordance with NFPA 255, Standard Method of Test of Surface Burning
Characteristics of Building Materials, extended for an additional 20
minutes
in the form in which they are installed, shall not require sprinkler
protection.

I believe this is the criteria by which the fire retardant needs to be
judged. Is that correct? What is the "additional 20 minutes" that is
being
referred to? I will be taking a closer look at NFPA 255. But meanwhile
if
there is anyone who has already gone through this process, I would
appreciate any comments.

Tony

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email
to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to