look in your Building Code for how much people space you need. make
the other stuff not encroach in that.

On Wed, Dec 1, 2010 at 12:47 PM, Daniel Wilder <[email protected]> wrote:
> 14 '10 Edition
>
> 7.3.1.1 Hose connections and hose stations shall be unobstructed and shall
> be located not less than 3 ft or more than 5ft above the floor.
> 7.3.1.2 The hose conneciton chall not be obstructed by the closed or open
> door or other objects on the landing.
>
>
> -----Original Message-----
> From: [email protected]
> [mailto:[email protected]] On Behalf Of Brian Harris
> Sent: Wednesday, December 01, 2010 1:32 PM
> To: [email protected]
> Subject: Standpipe Clearances
>
> I've searched through 13,14,& the archives and don't see anything that talks
> about required clearances around standpipes in stairways. I'm working on a
> parking garage/office complex and the Architect wants to create a "niche" in
> the wall behind the door for the standpipe & drain. My concern is that when
> the door is open into the stairwell it will block access to the standpipe,
> any input would be greatly appreciated.
>
>
>
> Brian Harris
>
> First Defense Fire Protection
>
> 11957 Ramah Church Road
>
> Huntersville, NC 28078
>
> Phone: 704.948.3506
>
> Fax: 704.948.3507
>
> Nicet # 128476
>
>
>
>
>
>
>
> =======
> Email scanned by PC Tools - No viruses or spyware found.
> (Email Guard: 7.0.0.21, Virus/Spyware Database: 6.16420)
> http://www.pctools.com/
> =======
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
AFSA, SFPE, ASCET, NFPA, NFSA, AFAA, ASEE, NIBS, WSAFM, WFC

They are happy men whose natures sort with their vocations. -Francis
Bacon, essayist, philosopher, and statesman (1561-1626)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to