Yes, because per the definitions in NFPA-13, rack storage IS high piled storage.

3.9.1.17 High-Piled Storage. Solid-piled, palletized, *rack storage*, bin box, and shelf storage in excess of 12 ft (3.7 m) in height.

Reference is from the 2010 edition.
PARSLEY CONSULTING
Ken Wagoner, SET
760.745.6181 voice
760.745.0537 fax
[email protected] <mailto:[email protected]>e-mail
www.ParsleyConsulting.com <http://www.ParsleyConsulting.com>website


On 12/2/2010 3:03 PM, Ryan Peterson wrote:
NFPA 13 2002 edition

Does table 8.6.2.2.1(d) apply to rack storage? (not just high piled storage as 
the table is titled)

Thank you,

Ryan Peterson
Wayne Automatic Fire Sprinklers
Office 407-877-5593



_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to