We have doubts regarding criteria for protection of the following:

Class III, solid pile
Storage height: up to 20 ft
Máximum building height 30 ft
NFPA 13 2010 Edition

As we understand, the code gives two options which are:

1) Per 14.2.4, Control Mode Density Area:Figure 14.2.4.2  With ordinary 
temperature, K=11,2 sprinkler we need  0,215 gpm/sq ft over 2000 sq ft. Flow 
rate equals 430 gpm

2) If we go to 14.3, Control Mode Specific Application, Table 14.3.1, for same 
conditions, we are required to have 15 sprinklers with  K= 11,2 operating with 
a minimum discharge pressure of 25 psi. Flow rate equals 840 gpm and density is 
0,43 gpm/sq.ft.

Are both cases valid for the hazard we are protecting?

Why such a large difference in terms of flow and density?

Best regards and thanks in advance

J.P. Merlino