Rod, I have had non-dry pend on return bends approved on pre-action because the pipe and heads where in heated areas, and can say I have seen nothing in UFC that goes counter to 13 in that regard.
-----Original Message----- From: Rod DiBona [mailto:[email protected]] Sent: Tuesday, January 11, 2011 11:42 AM To: [email protected] Subject: UFC 3-600 return bends? Does anyone know off hand if return bends are allowed in the UFC 3-600? I had it in my mind that dry pendants were mandated in all dry and preaction systems but cannot locate the reference. Maybe another standard?? Maybe I am just going crazy. Thanks. Rod DiBona Rapid Fire _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)