I'm doing one right now with a 3:12 I inquired with our very experienced foam 
FPE and he said no increase.  Now we didn't get fully into it but in a nut 
shell there is no requirement.  13 is not used.  My thinking is the sprinklers 
are a water based heat detection system.  The HEF is what will control the fire 
or not.  Also I just learned HEF has never been tested for this application.

Chris
-----Original Message-----
From: Mark Sornsin <[email protected]>
Sender: [email protected]
Date: Tue, 11 Jan 2011 18:23:21 
To: [email protected]<[email protected]>
Reply-To: [email protected]
Subject: ETL 02-15 for Hi-Ex systems

All:

Do any of you with Air Force Hi-Ex Foam experience know if there is any reason 
NOT to increase the 5,000 sq.ft. design area  by 30% when you are under a 
sloped roof (4:12)?

Mark A. Sornsin, PE | Fire Protection Engineer
Ulteig Engineers, Inc. |Fargo, ND 
Direct:    701. 280.8591 | www.ulteig.com