Bobby-
I've argued passionately about what is the right way to approach some projects, 
like avoiding an ESFR system in a woodworking plant.
However, at some point you have to let go- if AHJ/FM accept, then the situation 
is "Approved" and you're done- short of donating the alarm system.

You can lead a horse to water but you can't make em smart.

George Church'
Rowe Sprinkler
[email protected]
570-837-7647

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Bobby Gillett
Sent: Wednesday, January 12, 2011 8:58 AM
To: [email protected]
Subject: RE: Fire Pump Monitoring

We are providing flow switches for future installation of alarms, but all 
valves will be "secured" and there is a mechanical water motor alarm servicing 
the systems. This was original and what owner has requested, AHJ/FM Global has 
approved this. I agree with, and have pushed for, alarm system and constant 
monitoring from bid time. It's not completely out, but the owner is still 
leading towards not doing this at this time.

 

Bobby Gillett

Sr. Project Manager

Key Fire Protection, Inc.

(731) 424-0130 office  (731) 424-9285 fax 

(731) 267-4853 cell

 <mailto:[email protected]>
[email protected]

 

 

  _____  

From: [email protected]
[mailto:[email protected]] On Behalf Of Todd Williams
Sent: Wednesday, January 12, 2011 7:50 AM
To: [email protected]
Subject: Re: Fire Pump Monitoring

 

Is there going to be waterflow monitoring on the sprinklers? If so, perhaps 
that service could be extended to include the pump. If there is not going to 
any monitoring on the sprinklers, you have a bigger problem. The AHJ may wisely 
not allow that.


At 08:33 AM 1/12/2011, you wrote:
>While we are on the subject of fire alarm controllers/monitoring; we 
>have a project where a company has bought an existing building and they 
>are upgrading for their use. Part of the FP upgrade is the need for a 
>fire
pump.
>The owner is not going to install an alarm system for the property at 
>this time. Every fire pump I have ever done, the facility was equipped 
>with
alarm
>monitoring. What are some options for the owner to achieve the required 
>notifications without alarm system? I am waiting to hear from the owner 
>to see if someone will be on site 24/7 (third shift, night maint., 
>etc.). I do realize his best option is to provide alarms/alarm 
>monitoring but I do not think he will proceed this route. Just trying 
>to get a heads up as I know they will ask for options.
>
>
>
>Thank you,
>
>
>
>Bobby Gillett
>
>Sr. Project Manager
>
>Key Fire Protection, Inc.
>
>(731) 424-0130 office  (731) 424-9285 fax
>
>(731) 267-4853 cell
>
>  <mailto:[email protected]>
>[email protected]
>
>
>
>
>
>
>
>_______________________________________________
>Sprinklerforum mailing list
>[email protected]
>http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
>For Technical Assistance, send an email to: [email protected]
>
>To Unsubscribe, send an email 
>to:[email protected]
>(Put the word unsubscribe in the subject field)

Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

  _____  

No virus found in this message.
Checked by AVG - www.avg.com
Version: 10.0.1191 / Virus Database: 1435/3374 - Release Date: 01/11/11

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to