It always does help, John, thanks, far more than 'stay out of the air space'...). I wanted to add for Brian's sake of the original post- it sounded like he had the many small electrical closets in mind- I offset around them and stub in a sidewall on my way by. I consider them OHI, and so I can use standard response, intermediate temp. For the big elect. rooms, (and elevator equipment) I go in once and never come out :)
-----Original Message----- From: John Drucker [mailto:[email protected]] Sent: Sunday, January 30, 2011 6:37 AM To: [email protected] Subject: FW: Electrical Rooms-Dedicated Equipment Space,Sprinklers and IBC Exemptions Members, Sprinkler piping is permitted in and through electrical rooms with two provisions, first the piping cannot be located in the dedicated electrical space, and second watersheds or other protective devices must be provided for electrical equipment below when piping is located above the dedicated electrical space. The National Electrical Code (NEC) does not prohibit the installation of fire sprinklers in electrical rooms, the 2006 and 2009 Editions of the IBC reinforce the sprinkler requirements; 903.3.1.1.1 Exempt locations. "Automatic sprinklers shall not be required in the following rooms or areas where such rooms or areas are protected with an approved automatic fire detection system in accordance with Section 907.2 that will respond to visible or invisible particles of combustion. SPRINKLERS SHALL NOT BE OMITTED FROM ANY ROOM MERELY BECAUSE IT is damp, of fire-resistance-rated construction OR CONTAINS ELECTRICAL EQUIPMENT." However the 2006 and 2009 IBC provides the following sprinkler exemption for separated and detected GENERATOR AND TRANSFORMER rooms; 903.3.1.1. - 3. "GENERATOR AND TRANSFORMER ROOMS separated from the remainder of the building by walls and floor/ceiling or roof/ceiling assemblies having a fire-resistance rating of NOT LESS THAN 2 HOURS." Keep in mind where this exemption is utilized a fire alarm system pursuant to 907.2 utilizing smoke detectors located in the generator and or transformer room(s) must be installed which means the space must be suitable for smoke detectors in accordance with the products listing and NFPA-72. Hope this helps, John Drucker, CET Fire Protection Subcode Official Fire/Building/Electrical Inspector Not the official position of any agency, association, committee or otherwise. Obtain required applications, permits, inspections and approvals from Authority(s) Having Jurisdiction. -----Original Message----- Sent: Saturday, January 29, 2011 7:55 PM Subject: RE: Electrical Rooms 2008 NFPA-70 (NEC) 110.26(F) (F) Dedicated Equipment Space. All switchboards, panelboards, distribution boards, and motor control centers shall be located in dedicated spaces and protected from damage. (1) Indoor. Indoor installations shall comply with 110.26(F)(1)(a) through (F)(1)(d). (a) Dedicated Electrical Space. The space equal to the width and depth of the equipment and extending from the floor to a height of 1.8 m (6 ft) above the equipment or to the structural ceiling, whichever is lower, shall be dedicated to the electrical installation. No piping, ducts, leak protection apparatus, or other equipment foreign to the electrical installation shall be located in this zone. Exception: Suspended ceilings with removable panels shall be permitted within the 1.8-m (6-ft) zone. (b) Foreign Systems. The AREA ABOVE THE DEDICATED SPACE required by 110.26(F)(1)(a) SHALL BE PERMITTED TO CONTAIN FOREIGN SYSTEMS, provided PROTECTION IS INSTALLED to avoid damage to the electrical equipment from condensation, LEAKS, OR BREAKS IN SUCH FOREIGN SYSTEMS. (c) Sprinkler Protection. Sprinkler PROTECTION shall be permitted for the dedicated space where the piping complies with this section. (d) Suspended Ceilings. A dropped, suspended, or similar ceiling that does not add strength to the building structure shall not be considered a structural ceiling. In other words the dedicated equipment space is a three dimensional exclusion zone above and around switchboards, panelboards, distribution boards, and motor control centers which is reserved for electrical wiring only. The space begins at the floor, the width and depth of the equipment and to a height of 6ft above the equipment or to the STRUCTURAL ceiling whichever is LOWER. So keep out unless you're the electrician. Take heed of (C), the operative term is PROTECTION not PIPING. So you can spray water in the dedicated space, just don't run the pipe in there. Hope this helps, John Drucker, CET Fire Protection Subcode Official Fire/Building/Electrical Inspector Not the official position of any agency, association, committee or otherwise. Obtain required applications, permits, inspections and approvals from Authority(s) Having Jurisdiction. _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)