Stewart,

I laboured over this posting. I wanted to colour it appropriately. Mr.
Boswel(l) in particular was taxing. The double L spelling did not look
proper, but neither did the single. A conundrum. Perhaps I should have
dropped him from my list but I wanted someone known to be as
punctilious a wordsmith as he. I would have chosen Mr. Churchill
except for all those other minor things he did that would tend to
muddy my point. I chose poorly. Now if you don't mind, as George
pointed out I'm tired from standing, so I'll sit corrected. One learns
a lot being in error.

On Sun, Jan 30, 2011 at 11:58 PM, Stewart Kidd
<[email protected]> wrote:
> Tut, tut, Ron !
>
> Boswell has two 'll's' !
>
> (Dr Johnson wuld not mind  - his spelin wos atroshious)
>
> Stewart (MA and MSc)
>
>
> On 31 Jan 2011, at 00:28, Ron Greenman wrote:
>
>> John,
>>
>> Not at all. I believe I asked for your further input regarding my comments. 
>> To stand corrected is to admit learning in the face of preconceived notions. 
>> The learning is good for us unwashed, the validation let's you know that 
>> your efforts are appreciated, and the suggested lesson for the egotists is 
>> pretty clear, though it may escape them due to their nature. If any 
>> apologies are required it's from the developers of this form of 
>> communication wherein there is no place for even inflection. Were that we 
>> were all Voltaire, Twain, or Faulkner and there'd be no misunderstandings of 
>> this kind. But, alas, the art of letter writing is long dead. Modern Boswels 
>> compiling the emails of even famous scientists could easily title the work 
>> "The Collected Grocery Lists of Dr. X." When it cost a man a week's pay to 
>> send a letter because it absolutely, positively had to get there in a couple 
>> of months folks were a little more erudite. I believe I'm near the last 
>> graduating class where penmanship, spelling, punctuation, and an adherence 
>> to grammar were necessary for the educated man. The term for an educated 
>> person used to be knowledge of Arts, Letters and the Sciences.
>>
>> Ron Greenman
>> ...On the phone
>>
>> On Jan 30, 2011, at 2:11 PM, "John Drucker" <[email protected]> wrote:
>>
>>> Ron,
>>>
>>> Didn't mean for it to come across that way, just trying to help out
>>>
>>> John
>>>
>>> -----Original Message-----
>>> From: [email protected]
>>> [mailto:[email protected]] On Behalf Of Ron Greenman
>>> Sent: Sunday, January 30, 2011 1:08 PM
>>> To: [email protected]
>>> Subject: Re: Electrical Rooms-Dedicated Equipment Space, Sprinklers and IBC
>>> Exemptions
>>>
>>> I stand corrected. Although I haven't spent enough time with this to
>>> know how corrected I've been but there's enough easily assimilable to
>>> know I've been at least somewhat corrected. Thank you once again.
>>>
>>> On Sun, Jan 30, 2011 at 9:49 AM, John Drucker <[email protected]>
>>> wrote:
>>>> Fear not for the answer you seek is found in the code
>>>> ...............Emphasis in CAPS
>>>>
>>>> 2008 NFPA-70 (NEC)
>>>>
>>>> 110.26(F) Dedicated Equipment Space.
>>>> "All SWITCHBOARDS, PANELBOARDS, DISTRIBUTION BOARDS, AND MOTOR CONTROL
>>>> CENTERS shall be located in dedicated spaces and protected from damage."
>>>>
>>>> Article 100 Definitions
>>>>
>>>> Motor Control Center. An assembly of one or more enclosed sections having
>>> a
>>>> common power bus and PRINCIPALLY CONTAINING MOTOR CONTROL UNITS.
>>>>
>>>> Panelboard. A single panel or group of panel units designed for assembly
>>> in
>>>> the form of a single panel, including buses and automatic overcurrent
>>>> devices, and equipped with or without switches FOR THE CONTROL OF LIGHT,
>>>> HEAT, OR POWER CIRCUITS; designed to be placed in a cabinet or cutout box
>>>> placed in or against a wall, partition, or other support, and ACCESSIBLE
>>>> ONLY FROM THE FRONT.
>>>>
>>>> Switchboard. A large single panel, frame, or assembly of panels on which
>>> are
>>>> mounted on the face, back, or both, SWITCHES, OVERCURRENT AND OTHER
>>>> PROTECTIVE DEVICES, BUSES, and usually instruments. Switchboards are
>>>> GENERALLY ACCESSIBLE FROM THE REAR AS WELL as from the front and are not
>>>> intended to be installed in cabinets.
>>>>
>>>> No definition for Distribution Boards......let's see if another article
>>>> provides the answer..........
>>>>
>>>> 408.1 Scope. “This article covers the following: (1) All switchboards,
>>>> panelboards, and DISTRIBUTION BOARDS INSTALLED FOR THE CONTROL OF LIGHT
>>> AND
>>>> POWER CIRCUITS.”
>>>>
>>>> 90.3 Code Arrangement. “This Code is divided into the introduction and
>>> nine
>>>> chapters, as shown in Figure 90.3. CHAPTERS 1, 2, 3, AND 4 APPLY
>>> GENERALLY.”
>>>>
>>>> And last but not least, an online resource with descriptions, photos, etc
>>> of
>>>> panelboards, distribution boards from NEMA
>>>>
>>>> http://www.nema.org/prod/be/lvde/panelboard/enclose-pd/
>>>>
>>>> Hope this helps,
>>>>
>>>> John Drucker, CET
>>>> Fire Protection Subcode Official
>>>> Fire/Building/Electrical Inspector
>>>> Fire Marshals Office
>>>> Borough of Red Bank, NJ
>>>>
>>>> Not the official position of any agency, association, committee or
>>>> otherwise.  Obtain required applications, permits, inspections and
>>> approvals
>>>> from Authority(s) Having Jurisdiction.
>>>>
>>>>
>>>> -----Original Message-----
>>>> From: [email protected]
>>>> [mailto:[email protected]] On Behalf Of Ron
>>> Greenman
>>>> Sent: Sunday, January 30, 2011 11:07 AM
>>>> To: [email protected]
>>>> Subject: Re: Electrical Rooms-Dedicated Equipment Space, Sprinklers and
>>> IBC
>>>> Exemptions
>>>>
>>>> Brad,
>>>>
>>>> I'll defer to John if he calls me on this, but I don't think those
>>>> little electrical closets with a single lighting/general purpose
>>>> sub-panel, a mop sink, and the custodian's collection of porn really
>>>> count at all, and certainly not for sprinklers.
>>>>
>>>> On Sun, Jan 30, 2011 at 8:01 AM, Brad Casterline
>>>> <[email protected]> wrote:
>>>>> It always does help, John, thanks, far more than 'stay out of the air
>>>>> space'...). I wanted to add for Brian's sake of the original post- it
>>>>> sounded like he had the many small electrical closets in mind- I offset
>>>>> around them and stub in a sidewall on my way by. I consider them OHI, and
>>>> so
>>>>> I can use standard response, intermediate temp. For the big elect. rooms,
>>>>> (and elevator equipment) I go in once and never come out :)
>>>>>
>>>>> -----Original Message-----
>>>>> From: John Drucker [mailto:[email protected]]
>>>>> Sent: Sunday, January 30, 2011 6:37 AM
>>>>> To: [email protected]
>>>>> Subject: FW: Electrical Rooms-Dedicated Equipment Space,Sprinklers and
>>> IBC
>>>>> Exemptions
>>>>>
>>>>> Members,
>>>>>
>>>>> Sprinkler piping is permitted in and through electrical rooms with two
>>>>> provisions, first the piping cannot be located in the dedicated
>>> electrical
>>>>> space, and second watersheds or other protective devices must be provided
>>>>> for electrical equipment below when piping is located above the dedicated
>>>>> electrical space.
>>>>>
>>>>> The National Electrical Code (NEC) does not prohibit the installation of
>>>>> fire sprinklers in electrical rooms, the 2006 and 2009 Editions of the
>>> IBC
>>>>> reinforce the sprinkler requirements;
>>>>>
>>>>> 903.3.1.1.1 Exempt locations. "Automatic sprinklers shall not be required
>>>> in
>>>>> the following rooms or areas where such rooms or areas are protected with
>>>> an
>>>>> approved automatic fire detection system in accordance with Section 907.2
>>>>> that will respond to visible or invisible particles of combustion.
>>>>> SPRINKLERS SHALL NOT BE OMITTED FROM ANY ROOM MERELY BECAUSE IT is damp,
>>>> of
>>>>> fire-resistance-rated construction OR CONTAINS ELECTRICAL EQUIPMENT."
>>>>>
>>>>> However the 2006 and 2009 IBC provides the following sprinkler exemption
>>>> for
>>>>> separated and detected GENERATOR AND TRANSFORMER rooms;
>>>>>
>>>>> 903.3.1.1. - 3. "GENERATOR AND TRANSFORMER ROOMS separated from the
>>>>> remainder of the building by walls and floor/ceiling or roof/ceiling
>>>>> assemblies having a fire-resistance rating of NOT LESS THAN 2 HOURS."
>>>>>
>>>>> Keep in mind where this exemption is utilized a fire alarm system
>>> pursuant
>>>>> to 907.2 utilizing smoke detectors located in the generator and or
>>>>> transformer room(s) must be installed which means the space must be
>>>> suitable
>>>>> for smoke detectors in accordance with the products listing and NFPA-72.
>>>>>
>>>>> Hope this helps,
>>>>>
>>>>> John Drucker, CET
>>>>> Fire Protection Subcode Official
>>>>> Fire/Building/Electrical Inspector
>>>>>
>>>>> Not the official position of any agency, association, committee or
>>>>> otherwise.  Obtain required applications, permits, inspections and
>>>> approvals
>>>>> from Authority(s) Having Jurisdiction.
>>>>>
>>>>> -----Original Message-----
>>>>> Sent: Saturday, January 29, 2011 7:55 PM
>>>>> Subject: RE: Electrical Rooms
>>>>>
>>>>> 2008 NFPA-70 (NEC) 110.26(F)
>>>>>
>>>>> (F) Dedicated Equipment Space. All switchboards, panelboards,
>>> distribution
>>>>> boards, and motor control centers shall be located in dedicated spaces
>>> and
>>>>> protected from damage.
>>>>>
>>>>> (1) Indoor. Indoor installations shall comply with 110.26(F)(1)(a)
>>> through
>>>>> (F)(1)(d).
>>>>>
>>>>> (a) Dedicated Electrical Space. The space equal to the width and depth of
>>>>> the equipment and extending from the floor to a height of 1.8 m (6 ft)
>>>> above
>>>>> the equipment or to the structural ceiling, whichever is lower, shall be
>>>>> dedicated to the electrical installation. No piping, ducts, leak
>>>> protection
>>>>> apparatus, or other equipment foreign to the electrical installation
>>> shall
>>>>> be located in this zone.
>>>>>
>>>>> Exception: Suspended ceilings with removable panels shall be permitted
>>>>> within the 1.8-m (6-ft) zone.
>>>>>
>>>>> (b) Foreign Systems. The AREA ABOVE THE DEDICATED SPACE required by
>>>>> 110.26(F)(1)(a) SHALL BE PERMITTED TO CONTAIN FOREIGN SYSTEMS, provided
>>>>> PROTECTION IS INSTALLED to
>>>>> avoid damage to the electrical equipment from condensation, LEAKS, OR
>>>> BREAKS
>>>>> IN SUCH FOREIGN SYSTEMS.
>>>>>
>>>>> (c) Sprinkler Protection. Sprinkler PROTECTION shall be permitted for the
>>>>> dedicated space where the piping complies with this section.
>>>>>
>>>>> (d) Suspended Ceilings. A dropped, suspended, or similar ceiling that
>>> does
>>>>> not add strength to the building structure shall not be considered a
>>>>> structural ceiling.
>>>>>
>>>>>
>>>>> In other words the dedicated equipment space is a three dimensional
>>>>> exclusion zone above and around switchboards, panelboards, distribution
>>>>> boards, and motor control centers which is reserved for electrical wiring
>>>>> only. The space begins at the floor, the width and depth of the equipment
>>>>> and to a height of 6ft above the equipment or to the STRUCTURAL ceiling
>>>>> whichever is LOWER. So keep out unless you're the electrician.
>>>>>
>>>>> Take heed of (C), the operative term is PROTECTION not PIPING. So you can
>>>>> spray water in the dedicated space, just don't run the pipe in there.
>>>>>
>>>>> Hope this helps,
>>>>>
>>>>> John Drucker, CET
>>>>> Fire Protection Subcode Official
>>>>> Fire/Building/Electrical Inspector
>>>>>
>>>>> Not the official position of any agency, association, committee or
>>>>> otherwise.  Obtain required applications, permits, inspections and
>>>> approvals
>>>>> from Authority(s) Having Jurisdiction.
>>>>>
>>>>>
>>>>> _______________________________________________
>>>>> Sprinklerforum mailing list
>>>>> [email protected]
>>>>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>>>>
>>>>> For Technical Assistance, send an email to: [email protected]
>>>>>
>>>>> To Unsubscribe, send an email to:[email protected]
>>>>> (Put the word unsubscribe in the subject field)
>>>>>
>>>>> _______________________________________________
>>>>> Sprinklerforum mailing list
>>>>> [email protected]
>>>>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>>>>
>>>>> For Technical Assistance, send an email to: [email protected]
>>>>>
>>>>> To Unsubscribe, send an email to:[email protected]
>>>>> (Put the word unsubscribe in the subject field)
>>>>>
>>>>
>>>>
>>>>
>>>> --
>>>> Ron Greenman
>>>> Instructor
>>>> Fire Protection Engineering Technology
>>>> Bates Technical College
>>>> 1101 So. Yakima Ave.
>>>> Tacoma, WA 98405
>>>>
>>>> [email protected]
>>>>
>>>> http://www.bates.ctc.edu/fireprotection/
>>>>
>>>> 253.680.7346
>>>> 253.576.9700 (cell)
>>>>
>>>> Member:
>>>> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC
>>>>
>>>> They are happy men whose natures sort with their vocations. -Francis
>>>> Bacon, essayist, philosopher, and statesman (1561-1626)
>>>> _______________________________________________
>>>> Sprinklerforum mailing list
>>>> [email protected]
>>>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>>>
>>>> For Technical Assistance, send an email to: [email protected]
>>>>
>>>> To Unsubscribe, send an email to:[email protected]
>>>> (Put the word unsubscribe in the subject field)
>>>>
>>>> _______________________________________________
>>>> Sprinklerforum mailing list
>>>> [email protected]
>>>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>>>
>>>> For Technical Assistance, send an email to: [email protected]
>>>>
>>>> To Unsubscribe, send an email to:[email protected]
>>>> (Put the word unsubscribe in the subject field)
>>>>
>>>
>>>
>>>
>>> --
>>> Ron Greenman
>>> Instructor
>>> Fire Protection Engineering Technology
>>> Bates Technical College
>>> 1101 So. Yakima Ave.
>>> Tacoma, WA 98405
>>>
>>> [email protected]
>>>
>>> http://www.bates.ctc.edu/fireprotection/
>>>
>>> 253.680.7346
>>> 253.576.9700 (cell)
>>>
>>> Member:
>>> ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC
>>>
>>> They are happy men whose natures sort with their vocations. -Francis
>>> Bacon, essayist, philosopher, and statesman (1561-1626)
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>>
>>> For Technical Assistance, send an email to: [email protected]
>>>
>>> To Unsubscribe, send an email to:[email protected]
>>> (Put the word unsubscribe in the subject field)
>>>
>>> _______________________________________________
>>> Sprinklerforum mailing list
>>> [email protected]
>>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>>
>>> For Technical Assistance, send an email to: [email protected]
>>>
>>> To Unsubscribe, send an email to:[email protected]
>>> (Put the word unsubscribe in the subject field)
>> _______________________________________________
>> Sprinklerforum mailing list
>> [email protected]
>> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>>
>> For Technical Assistance, send an email to: [email protected]
>>
>> To Unsubscribe, send an email to:[email protected]
>> (Put the word unsubscribe in the subject field)
>
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Ron Greenman
Instructor
Fire Protection Engineering Technology
Bates Technical College
1101 So. Yakima Ave.
Tacoma, WA 98405

[email protected]

http://www.bates.ctc.edu/fireprotection/

253.680.7346
253.576.9700 (cell)

Member:
ASEE, SFPE, ASCET, NFPA, AFSA, NFSA, AFAA, NIBS, WSAFM, WFC

They are happy men whose natures sort with their vocations. -Francis
Bacon, essayist, philosopher, and statesman (1561-1626)
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to