Dewayne,

4-ft wide and 18-in. down is correct if the obstruction is in the middle of
the space where water can throw over the top of the obstruction.  However,
you also said the "canopies" protrude from the wall, so now the 4-ft wide
exemption does not apply.  Water cannot throw on both sides of the "canopy"
if it is against the wall.

Jeff Hewitt, PE, SET, SFPE (Professional Member)
Corporate Engineer
Bi-State Fire Protection Corporation

241 Hughes Lane
St. Charles, MO  63301
636-946-0011
636-946-5172 (fax)
314-574-6989 (cell)

Fire Sprinklers Save lives.
Can You Live Without Them?

-----Original Message-----
From: [email protected]
[mailto:[email protected]] On Behalf Of Dewayne
Martinez
Sent: Friday, February 18, 2011 3:56 PM
To: [email protected]
Subject: Canopy projecting from wall

I have a situation where I have a room with 18ft acoustical ceilings and
a couple of non-combustible canopies projecting from a wall around 9ft
AFF.
The canopies themselves protrude from the wall only 3ft and are about
8ft long each.  I don't think I would need additional protection below
the canopies since the overhead ceiling is fully sprinkled, the canopies
are less than 4ft wide and at least 18 down from the overhead
sprinklers, and no additional floor area is created.
What does the forum think?
Thanks,
Dewayne Martinez
Design Build Fire Protection
New Berlin, WI
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to