Dewayne, 4-ft wide and 18-in. down is correct if the obstruction is in the middle of the space where water can throw over the top of the obstruction. However, you also said the "canopies" protrude from the wall, so now the 4-ft wide exemption does not apply. Water cannot throw on both sides of the "canopy" if it is against the wall.
Jeff Hewitt, PE, SET, SFPE (Professional Member) Corporate Engineer Bi-State Fire Protection Corporation 241 Hughes Lane St. Charles, MO 63301 636-946-0011 636-946-5172 (fax) 314-574-6989 (cell) Fire Sprinklers Save lives. Can You Live Without Them? -----Original Message----- From: [email protected] [mailto:[email protected]] On Behalf Of Dewayne Martinez Sent: Friday, February 18, 2011 3:56 PM To: [email protected] Subject: Canopy projecting from wall I have a situation where I have a room with 18ft acoustical ceilings and a couple of non-combustible canopies projecting from a wall around 9ft AFF. The canopies themselves protrude from the wall only 3ft and are about 8ft long each. I don't think I would need additional protection below the canopies since the overhead ceiling is fully sprinkled, the canopies are less than 4ft wide and at least 18 down from the overhead sprinklers, and no additional floor area is created. What does the forum think? Thanks, Dewayne Martinez Design Build Fire Protection New Berlin, WI _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)