Todd,
If the combustible canopy attaches to the building anywhere it becomes a
fully protected item,not just the attachment area.If this were not the
case,then all the combustible walkways perpendicular to buildings could
be protected by dry sidewalls @ the point of connection.(My opinion)
Lamar Vaughn,SET
On Wed, Feb 23, 2011 at 11:44 AM, Todd Williams wrote:
I am designing a system for a restaurant. They have a covered outside
dining area and an L-shaped covered walkway accessing it. Construction
is combustible. The canopy for the dining area is about 5 ft from the
building (also wood construction), but is not attached. The canopy
abuts the building entrance. My thought is that the canopy needs to be
protected where it attached to the building, but does the full dining
area need protection? NFPA 13 (2002) and City of Houston Codes.
Todd G. Williams, PE
Fire Protection Design/Consulting
Stonington, CT
860.535.2080
www.fpdc.com