wait! Let's keep it very simple here:

Can you calculate a SP system that utilizes both a fixed Fire pump that feed
sprinklers and SP's and also use the FDC with the accompanying Fire Pumper
Truck and adajent fire hydrant as a SOURCE?

I think the answer is a resounding NO but I am willing to be wrong if there
is a loophole I am unfamiliar with...

Thanks,
Greg

On Mon, Mar 7, 2011 at 11:48 AM, George Church <[email protected]>wrote:

> Is the FDC connected to pump suction?
> If its not, and the pump is producing 150 PSI discharge, and the FD hits
> the FDC with 150 (connected to the discharge side of the fire pump), then
> you have 150 PSI, not 300, going to the system.
>
> You can graph the combination of dissimilar supplies by graphing both and
> adding the flows at same pressures.
>
> Safe to assume the large Fed entity has an FPE as EOR? Cause the FDC isn't
> exactly an "automatic" water supply, so the ice is thin, even if its up by
> the FroBros.
>
> George Church
> Rowe Sprinkler Systems, Inc.
> PO Box 407, Middleburg, PA 17842
> 877-324-ROWE       570-837-6335 fax
> [email protected]
>
>
>
> -----Original Message-----
> From: [email protected] [mailto:
> [email protected]] On Behalf Of Greg McGahan
> Sent: Monday, March 07, 2011 12:29 PM
> To: [email protected]
> Subject: Manual vs Auto SP
>
> What do you do with an existing SP system that far exceed the pressure
> requirement when performing calcs...nearly 200 psi over the curve due to the
> fact that you are flowing 1,250 gpm through 4" pipe.
>
> The owner wants to classify the system as MANUAL and utilize a FD to feed
> the system but  leave the fire pump connected. The system still does not
> work when using only the FDC feeding the system due to the fact that the FD
> only plans to utilize 2 each 2-1/2" hose to connect to the FDC.
>
> The owner - a large Federal Entity - wants to make this a HYBRID system
> utilizing the Fire Pump and the FDC combined. I can't find a correct way to
> do this...thoughts?
>
> Greg
>
> --
> Greg McGahan
> Living Water Fire Protection, LLC
> 1160 McKenzie Road
> Cantonment, FL 32533
> 850-937-1850
> fax 850-937-1852
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
> _______________________________________________
> Sprinklerforum mailing list
> [email protected]
> http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum
>
> For Technical Assistance, send an email to: [email protected]
>
> To Unsubscribe, send an email to:[email protected]
> (Put the word unsubscribe in the subject field)
>



-- 
Greg McGahan
Living Water Fire Protection, LLC
1160 McKenzie Road
Cantonment, FL 32533
850-937-1850
fax 850-937-1852
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

Reply via email to