While George's statement is true.... (you don't currently have to use a tank per NFPA 22).... My friend Pete Schwab asked me to forward this to the forum: If you can forward for me, I would appreciate it, The 2013 ROP for NFPA 13R indicates the following: 13R-72 Log #71 Recommendation 9.5 Water Tanks. Where a water tank is installed, the water tank shall be installed in accordance with NFPA 22. Substantiation: Currently, only pressure tanks are required to meet NFPA 22, All tanks should be installed in accordance with this important NFPA standard. Final Action: Accept. There were no negative ballots on the first go round of the paper ballot. Pete
It should be recognized that the above is the opinion of a member of the NFPA, and has not been processed as a formal interpretation in accordance with the NFPA Regulations Governing Committee Projects and should therefore not be considered, nor relied upon, as the official position of the the NFPA, nor any of their technical committees. Sincerely, Cecil Bilbo Academy of Fire Sprinkler Technology Champaign, IL 217.607.0325 www.sprinkleracademy.com [email protected] OUR STUDENTS SAVE LIVES!! > From: [email protected] > To: [email protected] > Date: Fri, 18 Mar 2011 17:04:00 -0400 > Subject: RE: Tank for 13R system > > No, 13R tanks don't need to be #22 ones, pump DOES need to be #20. > At least if a fire pump is provided, it has to be per 20....... > Someone here pointed out that looks like a LOT more wiggle room than any of > us had read into it previously. > > Better way if possible on dual purpose tanks is to come off above the level > of water reserved for sprinkler with the domestic so it can't steal the FP > water- so long as gravity is on. > Can't always arrange this way, but if you can, makes it more bulletproof. If > you couldn't, a low water alarm with intelligently placed or transmitted > signal should be acceptable on a 13R. Course I'm not your BCO, just a retired > alternate from last edition of 22. > > We've had a large well get outfitted with an automatically starting pump > sized for the 13R demand and the domestic demand of a large bathroom being > added (oil field worker dorm) so it was a nice little reliable water supply, > found acceptable to the AHJ. > > George Church > Rowe Sprinkler Systems, Inc. > PO Box 407, Middleburg, PA 17842 > 877-324-ROWE 570-837-6335 fax > [email protected] > > > > -----Original Message----- > From: [email protected] > [mailto:[email protected]] On Behalf Of Dewayne > Martinez > Sent: Friday, March 18, 2011 4:56 PM > To: [email protected] > Subject: RE: Tank for 13R system > > I don't believe so. NFPA 13R (07ed)6.6.3(3) is the only section that > references NFPA 22 and it is for a pressure tank. > 6.6.3(4)calls for "A stored water supply with an automatically operated pump" > as a valid water supply. > Also, the appendix notes that when the tank is used for both domestic and > fire protection, a low water alarm should be installed. > > Dewayne Martinez > Design Build Fire Protection > New Berlin, WI > > > > -----Original Message----- > From: [email protected] > [mailto:[email protected]] On Behalf Of Todd Williams > Sent: Friday, March 18, 2011 12:09 PM > To: [email protected] > Subject: Tank for 13R system > > Do tanks for 13R systems need to meet the requirements of NFPA 22? > Specifically, is an automatic fill system required? > > Todd G. Williams, PE > Fire Protection Design/Consulting > Stonington, CT > 860.535.2080 > www.fpdc.com > > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email > to:[email protected] > (Put the word unsubscribe in the subject field) > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) > _______________________________________________ > Sprinklerforum mailing list > [email protected] > http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum > > For Technical Assistance, send an email to: [email protected] > > To Unsubscribe, send an email to:[email protected] > (Put the word unsubscribe in the subject field) _______________________________________________ Sprinklerforum mailing list [email protected] http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: [email protected] To Unsubscribe, send an email to:[email protected] (Put the word unsubscribe in the subject field)