9.2.3.5.2.1 Where the maximum static or flowing pressure,
whichever is greater at the sprinkler, applied other than through
the fire department connection, exceeds 100 psi (6.9 bar) and a
branch line above a ceiling supplies sprinklers in a pendent position
below the ceiling, the cumulative horizontal length of an
unsupported armover to a sprinkler or sprinkler drop shall not
exceed 12 in. (305 mm) for steel pipe and 6 in. (152 mm) for
copper tube.

It says cumulative horizontal length. So, if you have 20" of total horizontal length, you need a hanger.

On 3/24/2011 1:40 PM, Shawn Chapman wrote:

Would a hanger be required on an armover such as described below?
System has 150 static, so the 12" rule comes into play (pendant head in ceiling...).  
center of tile job has a 10" armover piece of 1" coming off of the branchline (no 
hanger).
 From there, swing joint 90's and 10" of pipe w/ 90 down to head (also-no 
hanger).  I feel a hanger is required.  Any opinions?