Brother fitter, cumulative length of an armover is the total length from
threads
to end of fitting. If you have a 11 1/2" pipe nipple AO EOC you have a
cumulative length of over 12" which requires a hanger over 100 psi. Field talk,
if the measurement from threads to end of fitting is more than 12" you need a
hanger, not center, end of fitting. Go with what is cheaper, and allowed with
AHJ, for a hanger, a shotgun, 3/8 insert, quick bolt aka red head, TBC, Sammy,
etc. Sometimes you have to run a TOR with a nipple cap 4' to catch a bar joist
because of a 11" AO to get 12" Center of Tile. Check your work order to specify
what COT is permissable. Some COT jobs have a tolerance of up to 2" to 4" on
any
side to sell the job. Fitter make sure your COT lines up one way down a
corridor
or one big room with many heads. Give your customer the best work for their $.