I'd be very careful of the type of "Lattice" no many meet the intent of 3.7.2 
of 13, 2007.

3.7.2* Unobstructed Construction. Construction where beams,
trusses, or other members do not impede heat flow or water
distribution in a manner that materially affects the ability of
sprinklers to control or suppress a fire. Unobstructed construction
has horizontal structural members that are not
solid, where the openings are at least 70 percent of the
cross-section area and the depth of the member does not
exceed the least dimension of the openings, or all construction
types where the spacing of structural members exceeds
71⁄2 ft (2.3 m) on center.

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of Brian Harris
Sent: Monday, March 28, 2011 11:53 AM
To: [email protected]
Subject: Lattice

Quoting a job that has several small offices that have lattice ceilings, the
same type of lattice you would put around the bottom of a porch. The walls
do not go to the deck and there are upright heads throughout. Does anyone
see any reason for adding a pendent head below the lattice? It's probably
75% open.

 

Brian Harris

First Defense Fire Protection

11957 Ramah Church Road

Huntersville, NC 28078

Phone: 704.948.3506

Fax: 704.948.3507

Nicet # 128476

 





=======
Email scanned by PC Tools - No viruses or spyware found.
(Email Guard: 7.0.0.21, Virus/Spyware Database: 6.17080)
http://www.pctools.com/
=======
_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)

_______________________________________________
Sprinklerforum mailing list
[email protected]
http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum

For Technical Assistance, send an email to: [email protected]

To Unsubscribe, send an email to:[email protected]
(Put the word unsubscribe in the subject field)