I believe that it's 6' min from the edge not max.  2010 it's been reduced to 5' 
min.

BK

-----Original Message-----
From: [email protected] 
[mailto:[email protected]] On Behalf Of George Medina Jr
Sent: Wednesday, March 30, 2011 2:11 PM
To: [email protected]
Subject: Sprinkler protection 6' from the inside edge of the eave

Dear Forum,

 
NFPA-13 Sec. 8.6.4.1.4.3 requires sprinklers within 6' from the inside edge of 
the eave line, would it still be required if there was blocking between the 
joist or if they were separate compartments because of wood blocking? so that a 
fire does not easily travel from the eave to the concealed space?
 


George Medina Jr. 