NFPA 13, 2007 8.10.7.2.1.7* Sprinklers shall be permitted to be placed without regard to the blades of a ceiling fan, provided the plan view of the fan is at least 50 percent open.
A.8.10.7.2.1.7 The housing unit of the ceiling fan is expected to be addressed by the Four Times Rule. Dewayne, I just read something about this saying that they were inconsequential and could be ignored. I believe it's in the latest NFPA Journal but I don't have it here. And of course I may be remembering wrong and read it in Ladies Home Journal and they have no effect on baking. I get confused at times. _______________________________________________ Sprinklerforum mailing list Sprinklerforum@firesprinkler.org http://fireball.firesprinkler.org/mailman/listinfo/sprinklerforum For Technical Assistance, send an email to: supp...@firesprinkler.org To Unsubscribe, send an email to:sprinklerforum-requ...@firesprinkler.org (Put the word unsubscribe in the subject field)